Was fixing a broken twin florescent fitting today and came across something I couldn't work out.

First thing I did was measure the incoming voltage. At the fitting I measured L-E =190, N-E = 90v.

Scratched my head for a minute until I realized the Earth's coming in from the numerous (4) twin and Earth's didn't look right.

3 cpcs we're in a terminal block and the other cpc was direct into the fitting. I decided to try L-E at the terminal block and got 240v.

I sorted the wiring out so all the Earth's were in the fitting properly and all is good. However, I can't seem to grasp why the off readings. I was effectively measuring L-E (just the single cpc from a single t+e) when I got the odd readings but 240 when measured with the other Earth's.

Only thing I can think is either the single cpc was not connected to earth properly (poor connection) ??

Thoughts
 
  • Agree
Reactions: buzzlightyear
Some times a loose neutral gives voltage across neutral and earth
 
Some times a loose neutral gives voltage across neutral and earth

I thought that but once all cpcs we're connected together the readings we're normal
 
So long as the cpc on its own was not connected to earth then you would be measuring a floating voltage. The value would not really mean anything as there is no reference point for it.
 
  • Like
Reactions: DPG and gazdkw82
If the earth wire you were testing was not connectted to ground,
Then you were measuring "Ghost voltage".
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
~
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Strange voltage readings - broken earth
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
gazdkw82,
Last reply from
dmxtothemax,
Replies
7
Views
3,382

Advert