Need to supply a sub main in a farm mechanical workshop need to work out cable size earthing isolation want to have about 40 amp supply about 5 meters run on catinary just wondered what would people do. Already have 8 way board with 30ma at end of circuit
50A is borderline for 6mm. google AEI cables and use their cable finder wizard.it calcs VD as well could poss. get away with 6mm XLPE, allowing for diversity.10mm XLPE is rated 81A, be inclined to export earth from cut-out or you will have to RCD alll circuits to achieve disconnection times if TT.. 63A switch fuse at supply end (10mm) . CU and RCD/RCBOs workshop. bear in mind only sockets need RCD as long as other circuits are surface wired. (TN earting)
I would just string some 6mm twin+e enclosed in plastic conduit and tie it to the catenery wire
An swa cable would be better,but if it cant be buried,its weight on the catenary would outdo any advantages