Testing 2.5+1.5 socket ring, got r1 0.75ohm, rn 0.76ohm, r2 1.38ohm. Expected r2 is 1.25ohm (=0.75*2.5/1.5)...bit of a deviation. All CPC connections inspected appeared fine. Had a micrometer to hand (not calibrated admittedly) so measured conductors, live = 1.77mm dia, CPC=1.30mm which gives CSAs (pi * dia^2 / 4) of 2.46mm^2 and 1.32mm^2. Which gives predicted r2 of 1.40ohm (=0.75*2.46/1.32) which is satisfyingly bang on.

How bothered/interested would you be about that slightly undersized 1.32mm^2 CPC? Not sure what permitted tolerances on it are. Could do the adiabatic on it I suppose.
 
Testing 2.5+1.5 socket ring, got r1 0.75ohm, rn 0.76ohm, r2 1.38ohm. Expected r2 is 1.25ohm (=0.75*2.5/1.5)...bit of a deviation. All CPC connections inspected appeared fine. Had a micrometer to hand (not calibrated admittedly) so measured conductors, live = 1.77mm dia, CPC=1.30mm which gives CSAs (pi * dia^2 / 4) of 2.46mm^2 and 1.32mm^2. Which gives predicted r2 of 1.40ohm (=0.75*2.46/1.32) which is satisfyingly bang on.

How bothered/interested would you be about that slightly undersized 1.32mm^2 CPC? Not sure what permitted tolerances on it are. Could do the adiabatic on it I suppose.

may i suggest you get a life..........

;-)
 
Testing 2.5+1.5 socket ring, got r1 0.75ohm, rn 0.76ohm, r2 1.38ohm. Expected r2 is 1.25ohm (=0.75*2.5/1.5)...bit of a deviation. All CPC connections inspected appeared fine. Had a micrometer to hand (not calibrated admittedly) so measured conductors, live = 1.77mm dia, CPC=1.30mm which gives CSAs (pi * dia^2 / 4) of 2.46mm^2 and 1.32mm^2. Which gives predicted r2 of 1.40ohm (=0.75*2.46/1.32) which is satisfyingly bang on.

How bothered/interested would you be about that slightly undersized 1.32mm^2 CPC? Not sure what permitted tolerances on it are. Could do the adiabatic on it I suppose.
and just how `satisfied` were you with this nick?..

i hope you wern`t making tents....
 
Re: T&E CPC Estimated 12% Undersize...?

Useful to know, cheers.

- - - Updated - - -



Nah, I'm a cowboy, not an Indian. ;-)

thought i`d seen you before:


village-people.jpg
 
Too far mate, too far! :D

I know...but I had the time to spare and I'm a pernickety sod. So if you had an expected r2 1.25 and measured 1.38, what would you do? Ignore it? I could understand ignoring it if measured r2 was lower than expected, could be parallel path within the CPC ring connected at at least two points. But higher?
 
It could be anything. Reduction in CSA for example.I would make sure the Zs complies. If you want to be that ---- about it make a note on the EICR. But I think everything is fine and it's a bit unnecessary.
 

Reply to T&E CPC Estimated 12% Undersize...? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Doing an EICR on a top floor flat recently and run into an issue I often do - which is judging imperial sizes when they are larger than the...
Replies
22
Views
3K
Greetings. I tested an rfc and recorded the following results: r1 = 0.62 rN = 0.89 r2 = 1.45 The difference in r1 and rN indicate loose...
Replies
24
Views
3K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D
N
Just finished some testing at a roughly 30yr old 2 bed flat which has been vacant for a couple of years. Carried out usual 3-stage dead test for...
Replies
83
Views
7K
NickD
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock