I was wondering about earthing and bonding today.

We take a 10mm conductor and connect within 600mm for gas/water/oil etc, but quite often pipes in a bathroom or elsewhere have a bonding clamp on them with a cable taken from lights or sockets. In the case of the lights that probably means they have a connection to earth via a 1mm conductor (lets assume they have plastic pipes along the way somewhere so are not connected to the 10mm). I cant quite see how this is acceptable given that 10mm is required for bonding?

I realise if they are not extraneous and have an RCD then 4mm supplementary bonding is not required, but this is not supplementary bonding, it is a light circuit being used to bond the pipes!!?

Any suggestions?
 
It was to regulations before widespread use of rcd's - extraneous metalwork in bathroom needed coupling to the earthing of all circuits within the bathroom so it should be a 4mm if singles on its own but you can imagine the issue of fitting numerous 4mm into say a batten lampholder -gladly them days are done.
 
Supplementary bonding should connect together the earth connections of exposed conductive parts and extraneous conductive parts together.

Yes, so as to make sure they are at the same potential. These examples that I come across are simply an earth cable taken from a ceiling rose or light switch to a copper pipe in the bathroom with a bonding clamp on. But as Darkwood said, it looks like this was the practise before RCD's.
 
Last edited:
Yes, so as to make sure they are at the same potential. These examples that I come across are simply an earth cable taken from a ceiling rose or light switch to a copper pipe in the bathroom with a bonding clamp on. But as Darkwood said, it looks like this was the practise before RCD's.

Yes this changed when the 17th come out. The object is to ensure that potential differences in excess of 50 V between accessible metalwork cannot occur.
 
It ensures that if enough current can flow accross the SBC, disconnection will take place, the touch voltage may exceed 50V.

Cheers
 

Reply to taking earth cable from sockets of lights to earth water pipes in bathroom? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
900
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock