I had a case today where, if I'd not done things properly, I would have ended up with exactly the same outcome, just saved myself half an hour or so of my time.

Swapping a couple of horrible fancy ceiling lights for standard ceiling rose (landing) and integral LED light (bathroom). Upstairs lighting circuit protected by 6A RCBO, also supplies alarm. Always do tests before tinkering (unless recent credible cert), so quick IR test, (L+N) to E: tester voltage won't go above about 20V, sign of a very low IR. Continuity about 6kΩ N to E: surprised the RCBO not tripping! (RCD test ok).

Start with usual suspects.

- Make sure RCBO fully disconnected.
- Alarm system? Disconnect. No.
- Funny timer switch thing (guess the sort of thing you use when you're on holiday to make it look like you're in, fits on a standard pattress)? Disconnect. No.
- Outside light? No, spurred off socket circuit.
- Manky-looking bathroom fan? SFCU (DP). No.
- Ooh, some standard ceiling roses, easy to have a look? No, they all look good.
- Access to loft? Just about do-able. Poke head up. Looks neat and tidy, no evidence of vermin or joint boxes. Can't see everything though. Hmm.

Alright, I know how this works - break the circuit down. Where's easiest/best guess for roughly the middle? Yeah, probably the landing light. Well, I guess, since I'm meant to be replacing it anyway...

Dear lord. Apparently, the person who replaced the original ceiling rose didn't have any connector blocks. But they did manage to extract the uninsulated terminals from the old ceiling rose, and wrap them with (now very brittle) insulation tape. Rip it all out. 707MΩ. That'll do.

Same thing on the bathroom light, though wasn't contributing to the fault.

Thing is... not sure what I would do different next time.

Was part of a bigger job so the lost time could be absorbed. I really enjoy fault-finding, don't get me wrong. But when you're only doing a small job, doing the proper tests and revealing demons that you need to sort out can add a lot of time, relatively - I just feel a bit awkward, as I sometimes wonder if the client thinks I'm taking them for a ride. I guess building up the trust is the way to go.

Apologies for the Friday brain dump. Anyway - all sorted. :)
 
  • Like
Reactions: Rpa07
Not sure I understand Dave "tester wont go above 20V" Sorry Steve
 
i'd guess that his tester might see a low IR and then refuse to apply the normal 250V or 500V. just guessing.
 
Yeah, pretty much what telectrix said, sorry for the confusion, Pete. The tester displays the voltage it's applying while doing the test. If it doesn't ramp up to 250V or 500V, then it's a sign there's a low resistance.
 
  • Like
Reactions: Barry White
Blimey. I've had 3 shits today does that count?
I had Delhi Belly a couple of weeks ago after coming back from India. I chose to keep the details off the forum, but y'know, each to their own.
 
  • Like
Reactions: Rpa07
Yeah, pretty much what telectrix said, sorry for the confusion, Pete. The tester displays the voltage it's applying while doing the test. If it doesn't ramp up to 250V or 500V, then it's a sign there's a low resistance.
Right Ta
 
the tester is current limited to about 1mA so if there is a poor IR, the voltage drops. Good modern IR testers also display the terminal voltages, great for testing surge limiters...
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

happysteve

Broke Internet
Arms
~
Joined
Location
Nottingham
Website
http://www.dovecote-electrical.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Dovecote Electrical

Thread Information

Title
Tests before alterations
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
happysteve,
Last reply from
UKMeterman,
Replies
8
Views
2,023

Advert