OK, I'll come clean. The 2 red cables from the henley block, sealed by the meter change man in 2010 go to:

1. The load side of circuit #4

2. Goes to the ceramic connetor hidden behind the bottom of the MCB's and directly on to the "redundant" connector in the airing cupboard for the "off peak" immersion heater.

Which means with the main switch of the CU off, the redundant immersion FCU in the airing cupboard is live and the load side of circuit #4 is live

Nice. I kept my fingers away from those cables once I've confirmed this.

The resident called the DNO and they were sending out a bod from the "theft" department - but surely if it had been a "scam" to bypass the meter, the main switch RCD would have tripped immediately.

Things like this do make the job interesting!!

lol
 
OK, I'll come clean. The 2 red cables from the henley block, sealed by the meter change man in 2010 go to:

1. The load side of circuit #4

2. Goes to the ceramic connetor hidden behind the bottom of the MCB's and directly on to the "redundant" connector in the airing cupboard for the "off peak" immersion heater.

Which means with the main switch of the CU off, the redundant immersion FCU in the airing cupboard is live and the load side of circuit #4 is live

Nice. I kept my fingers away from those cables once I've confirmed this.

The resident called the DNO and they were sending out a bod from the "theft" department - but surely if it had been a "scam" to bypass the meter, the main switch RCD would have tripped immediately.

Things like this do make the job interesting!!

lol
I take it the owners havent had house long then?
Because if they knew nothing about it surely just remove and retail and give certificate?
 
I bet the two un metered tails each connect into two of the mcb`s which are off and they are serving something naughty in the property!! directly feeding whatever circuit is fed from the mcb?
 
With the new looking meter, henley block, brown tails and tags under the meter, these have obviously been replaced in the recent past. This is confirmed by the sticker dated 2 years ago. The shiny matching seals on everything suggest that the small red cables were put in the new henley block by a meter installer who didn't know what he was doing.

This does not however explain the dodgy wiring at the other end of the small red tails. It sounds like there are 2 immersion elements in the same cylinder which suggests there was originally a separate economy 7 supply. In this case there should have been a second main switch, either in a separate board or in a bottom half of the one in the photo. Perhaps an amateur tried to rejig it in the past to supply the immersion but gave up when it continually tripped the RCD. This could be why the main immersion is now described as redundant.

Without seeing the installation before the meter was replaced it is difficult to know whether they tried to bypass the meter or whether the meter meter guy didn't know what to do with the old night rate tails. Though I would have expected the night time supply to have had one large cable, not doubling up a lightweight cable.
 
most meter changers are in a rush, or on price.. (I know) so if we saw anything like that we didnt care.. Im going back 20 years so dont judge me now. but we were given minimum training then list after list of addresses. and if we did see somthing that was dodgy and report it, then all hell would break loose and end up costing us the rest of the day or longer in reports. and that ment money lost. so It wasnt worth my wages to report somthing that had been like it for years. oh and for testing we were given a martindale to check at a socket when we had finished..

That was 20 years ago Please dont judge me :)
 

Reply to Todays EICR - can you spot the mistake? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
275
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
I am never quite sure if I am doing too little or too much when someone has a flood and I am called in. The most recent example is a chap has had...
Replies
4
Views
830

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock