Hmmmm I don't think so...

Stick with the dedicated SY glands...

Sent from my Xperia S using next doors WIFI

i know you should use the correct part designed for the job but always thought the ring in the external swa gland would tighten up on the taper enough to hold the braiding in the swa cable, therefore the braid would be held on earthed.
I maybe and probably wrong but was always under the impression that the correct sy glands are expensive?
opening my self up for abuse now, I've never had to use sy cable so ill stand corrected
 
Unlikely, as the braiding is a lot thinner than SWA.
I've used some glands, that will tighten up all the way on SWA, they would stand a chance with SY.
 
i've never actually seen one of these glands, i use the method where you seperate the strands then twist together, wrap with earth pvc tape and put a lug on it.
 
The sy glands actually clamp the braid the same as a swa gland. It's just that it uses a rubber grommet to clamp the braid to the steal cone. But there are some that just work like a brass to rubber, in which case you would put a lug on it and earth it. That's probably the best way as unless they clean up the area of paint it might not earth proper anyway.in either case it should be earthed which would eliminate the voltage or show a fault in the cable which you could pick up with a insulation tester between e cores and the earth.
 
And the only one to use.
Secures the cable properly and earths the braid, with a flying lead if need be.
 
It is possible to use a CW or E1W gland on SY. If you double the braid over at the end where the olive sits, it clamps the braid to the body of the gland. I've used it before and wouldn't hesitate to use it again. A tug test is a good idea, before the back compression seal is tightened.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
shotton, flintshire

Thread Information

Title
touch voltage help
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Dean Williams,
Last reply from
Brightspark2,
Replies
24
Views
3,370

Advert

Back
Top