Hi all. I installed a ring main the other day, and the breaker was a Type C 32A. I was wondering why the breaker was Type C and not B, as the circuit was feeding twin socket outlets in dado trunking, with only PCs and office stuff connected. This tends to be the case for all circuits where I work. I thought a Type C was for loads with a higher inrush current on startup. Any help appreciated. Cheers. Jim
 
Have you asked at work? what was your highest Zs reading for the ring final?
 
Hi Simon, max Zs was 0.51 Ohms. I haven't really been given a straight answer at work, so I thought I'd ask in here to see the typical scenarios where you would use Type C over a Type B for a ring main. Cheers. Jim
 
Well the maximum Zs for a C 32 is 0.72 ohms so disconnection times will be met for the circuit, what sort of environment does the ring serve?
 
The disconnection times were met, and I looked at the Type B, which was double the Zs value, so would have been well below. The circuit serves an office(3 x twin socket outlets) a fire alarm vacuum sensor, and a desk in the corridor(2xtwin socket outlets)
 
your boss probably has a surplus of type C.
 
  • Like
Reactions: 3 people
...either that tel, or like you oldies - his eyes might be going, and he thought it was a B...

Haha.

:leaving:
 
Some people think that if it ain't in a domestic board they need to type C the lot. In reality, they are just poor designers most of the time.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

jimmyray

Trainee
~
Joined
Location
Exeter

Thread Information

Title
Type of Breaker
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
jimmyray,
Last reply from
jimmyray,
Replies
8
Views
156

Advert