Discuss un-balanced three phase system in the UK Electrical Forum area at ElectriciansForums.net
hi i was hoping to get some help with a question please.
why does the current flow in the neutral when the three phase system is un-balanced?
is it to do with the fact when you have an unbalance between the phases the difference of current between the phases that causes excess current will then flow into the neutral?
OK. The only real way of getting your head into and around this is to go right back to the start: How is electricity generated, what actually happens when the rotor starts spinning inside the coils?
Picture the extreme case of unbalance where there is no load on two of the phases. You'll then have the same situation as a single phase supply with equal current in the line and neutral. Now if you increase the load on the other two phases, the neutral current will fall (to zero if it's fully balanced).
To calculate the neutral
I[SUB]n[/SUB] = √((I[SUB]a[/SUB]²+I[SUB]b[/SUB]²+I[SUB]c[/SUB]²)-((I[SUB]a[/SUB]*I[SUB]b[/SUB])+(I[SUB]a[/SUB]*I[SUB]c[/SUB])+(I[SUB]b[/SUB]*I[SUB]c[/SUB])))
And another thing. How can you be an approved electrician and a trainee at the same time?
firstly thankyou for taking time to reply
the approved and trainee who gives a hoot lol just me i suppose not very good with computers i posted the question then realized posted it in the wrong place mate i did not think ppl would get so excited with silly mistakes lol
like i said thanks for the reply pal
lol if i ask a question do i have to also justify if im an approved sparky lol
another think mate don't bother answering a question if it seems to upset you what is the point of the forum if you start to question if people are approved or not i reckon you should put the sheriff badge away and remember the forum was designed to help folk not to have you sit there and judge ppl lol
im sorry i posted the question did not think id upset superstar like lol
And if you're an approved electrician, why don't you 'get' the fundamentals of three phase?
Easy tiger, you've just added four posts to your total!
It's hard to answer the OP without a diagram, but If you think of a three phase motor that has no neutral, all phases are balanced as there are three identical windings. If one of the three phases was a greater load than the other two, the current has to return via the neutral.
whats that got to do with me being a spark lol i asked a question if you can answer cool if not what the sillyness has me being a spark got to do with anything lol maybe i should know its stuff i did years ago but life is such some times you forget the most basic but if you read the question i asked i had given the answer to my question too lol
please tell me do folk like you sit on these forums have nothing useful to add and talk garbage lol
Calm down, my first paragraph was in reply to Handysparks who had given four near consecutive replies.
I think you've jumped as my reply was posted a few seconds after yours!
I think the OP needs to give an explanation.
Reply to un-balanced three phase system in the UK Electrical Forum area at ElectriciansForums.net
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...