Gents, Im not the most technically minded electrician in the world but could someone explain why on commercial installations its necessary to fit 10ka mcbs not 6ka throughout the installation?
or mores the point, im being asked to fit a main panel and off that a few single phase domestic high integrity dbs, but use cheaper 6ka mcbs, which ive said no to.
ive read bs7671 434
Any help would be great.
 
Domestic usually single phase... commercial and industrial usually 3ph so a short circuit could be between 2 phases and thus approx twice that of a L - N or E fault, there is no specific requirement that says use 10Ka its more to be the result of the manufacturers designing them higher in their 3ph boards and in reality you only need to fit 10ka if your PFC could be larger than 6Ka.... and even then you still don't need a downstream device to meet this requirement if it is covered by an upstream device that meets the PFC requirements but its always good practice to fit the correct rated mcb's at any point in the circuit reqardless of upstream protection.
 
Lee, how can you measure or calc pfc, if the supply isn't installed yet?
it sounds like a 3pn in commercial so he could test at the head, i would be surprised if the ka warranted 10ka in a lot of commercial supplies but i could be wrong, im surprised there asking for three single phase boards though


is the cost much more thouh, i was under the impression there wasnt a lot in it
 
We use 10KA MCB's as a matter of course for all our general MCB DB's whether they are single or 3 phase DB's. For our substation lighting and small power DB's our MCB's are 25KA...
 
With commercial supplies they can be a large supply with short cable lengths which means far higher potential fault currents than a domestic supply.
 

Reply to use of 10ka mcbs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
523
I am drawing up a contract for a job in a domestic property which has a 3-phase Distribution Board and need to supply 3ph to a heat pump that's in...
Replies
3
Views
2K
Renewable energy startup is seeking a Technical Co-Founder to help create a company that is both socially and financially rewarding. The...
Replies
0
Views
1K
Electrician Jobs Domestic Electricians Wanted
RMS Facilities Management is looking for domestic electricians for the new build housing sector. Send your CVs to [email protected] Job title...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock