Hi,

This is the scenario;

The kitchen is now converted into a bedroom and there is a bathroom adjacent to that bedroom. The client asked me to re-route the 6mm cable and install a electric shower in the bathroom.

This is what I proposed to do:


  1. 8.5KW shower (8500/230=37 amps)
  2. 6mm T&E cable (current carrying capacity 46 amps, reference method C - Table 6E1 On-site Guide)
  3. 40A MCB

10mm would be ideal but 6mm is what I am given to play with.

Please, guys, let me know if I am being over ambitious!

Cheers!
 
In the OP it states 230V. Using 230V it works out at 6.22 Ώ. Use that with 240V and you will get 38.5A.
Nobody has changed ohm’s law. Same resistance with a higher voltage gives higher current. Simple?
 
well, i would always use 6mm , method C, up to 9kW.
 
buried in a masonry wall or uninsulated stud wall is still method C.
 
Not to cast aspersions on goodys clients but I'm guessing (know) to comply with fire/building regs (esp being given permission to turn a kitchen into a bedroom) a degree of insulation would be required
 
In the OP it states 230V. Using 230V it works out at 6.22 Ώ. Use that with 240V and you will get 38.5A.
Nobody has changed ohm’s law. Same resistance with a higher voltage gives higher current. Simple?

Ah yes of course simple, except for when I'm being an idiot. Thanks Tony.
 
Last edited by a moderator:

Reply to Using a 8.5KW shower on a 6mm circuit. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Shower circuit (40a mcb 10mm cable 8.5kw shower ) tripping after 5 mins RESET trips after 2 mins...changed shower /cable /isolator still tripping...
Replies
7
Views
564
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
733
Hi, I`m looking for an advice. I have an electric shower that I`m not using due to boiler changed to combi and added shower over bath feed by a...
Replies
1
Views
917
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
416

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock