I have just been carrying out an EICR and I have got some results that I am unsure about.
The property has 2 ovens on the same circuit, the circuit has a line-earth IR of 0.004Mohms when the cooker isolation switch of one of the ovens (oven 1) is closed, and 0.4Mohms when the other cooker isolation switch is closed and oven 1 switch is open Is there any reason that the electronics within an oven would cause this?
In the same area of the kitchen there are equally as bad IR results on the ring. The house has a very bad damp problem particularly in this area which I know is affecting the sockets but I was unsure with regards the electronics in an oven?
I realise this is an EICR but I will be carrying out the remedials over the next few days.
There is no RCD for the property.
Cheers all.
The property has 2 ovens on the same circuit, the circuit has a line-earth IR of 0.004Mohms when the cooker isolation switch of one of the ovens (oven 1) is closed, and 0.4Mohms when the other cooker isolation switch is closed and oven 1 switch is open Is there any reason that the electronics within an oven would cause this?
In the same area of the kitchen there are equally as bad IR results on the ring. The house has a very bad damp problem particularly in this area which I know is affecting the sockets but I was unsure with regards the electronics in an oven?
I realise this is an EICR but I will be carrying out the remedials over the next few days.
There is no RCD for the property.
Cheers all.