Hi, I am having weird behaviour from my flat's electrics which I think will need an electrician. The flat is empty whilst it is being redecorated and there is nothing plugged in.

With no load the RCD trips some days and will not reset but other times is fine. I have discovered that if I switch off the MCB for the 13A sockets in the bedroom and living room it will reset.

As it is an intermittent fault, even when there is no load, should I be suspecting the consumer unit or MCB? And if so will I need a new consumer unit or are replacement MCBs still available?

Sorry for all my questions but I would like to understand what is the likely problem, thank you, Simon
 
Hi - sorry to hear about the unexpected RCD trips. There are several things it could be and it will likely take a test instrument and an experienced operator to find it.

Hopefully there’s nothing wrong with the CU. I’m not familiar with the model number to comment on parts. Can you post a pic?
 
  • Like
Reactions: James and DPG
If it is empty and being decorated, it is possible that damp has got to some socket(s)

As above, it really needs someone with an insulation tester to trace the problem down to a particular point in the wiring.
 
  • Like
Reactions: DPG
Hi - sorry to hear about the unexpected RCD trips. There are several things it could be and it will likely take a test instrument and an experienced operator to find it.

Hopefully there’s nothing wrong with the CU. I’m not familiar with the model number to comment on parts. Can you post a pic?

Here is the consumer unit, its a MK one
 

Attachments

  • 20201006_104107.jpg
    20201006_104107.jpg
    125 KB · Views: 25
Hi - the modern MK version of those MCB and RCD can still be bought if required. I always advise turning the main switch off before taking the cover off - less surprises that way especially as we know there’s a fault somewhere :) .
 
If it is empty and being decorated, it is possible that damp has got to some socket(s)

As above, it really needs someone with an insulation tester to trace the problem down to a particular point in the wiring.
If it is empty and being decorated, it is possible that damp has got to some socket(s)

As above, it really needs someone with an insulation tester to trace the problem down to a particular point in the wiring.

Thanks, I know it does not test for insulation issues but I bought from Screwfix one of those socket testers, it was less than a tenner, more out of curiosity than anything. Anyway it showed that all the sockets were wired up correctly!! HOWEVER on one socket when I switched off the socket the tester buzzed very quietly which suggested to me (I'm no electrician) that something was amiss. I assume the positive was switched but where was the power coming from to make the tester buzz?? All speculations etc welcome, many thanks, Simon
[automerge]1602013676[/automerge]
Hi - the modern MK version of those MCB and RCD can still be bought if required. I always advise turning the main switch off before taking the cover off - less surprises that way especially as we know there’s a fault somewhere :) .

Yes sorry about that, I'm an oldie and should know better
 
  • Like
Reactions: Wilko

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Weird Electrium Consumer Unit B4471/2?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
SiFiSu,
Last reply from
SiFiSu,
Replies
5
Views
1,747

Advert