157
I came across this at a customer's place.

fuse.jpg

Semi - enclosed ceramic but it pre-dates BS3036. The iron break-out (yes it is is bonded..) enclosure is "Callender" branded and dates from when the house was built (1930's).

I will pull the fuse next visit and measure/check the wire diameter. I am expecting 60A but not sure. The Callender brand ceramic holder says "Carry 30, 60 blow" but that will be pretty meaningless. The customer says the fuse blew some years ago and was replaced. (I have checked - it does contain a fuse and not a nail.

I could replace the wire next visit with known 60A so I can correctly document it ? - But that belongs to DNO and not my bit to alter. Would you do this - or just rely on the Vernier & 533.1.1.3 ? DNO seemed happy with the fuse (by visual inspection only isofar as there was one!) without even checking it - see later.

60 A is adequate for the customer (with a little constructive diversity) and is limited to that anyway by 16mm tails to the meter.

I shall probably assume the worst-case for short-circuit capacity of newer BS3036 S1A type (ie 1KA). - This still covers me for the measured PFC.

Installation is TNS, lead sheathed supply cable with double layer spiral steel banding.

I had the DNO round before touching anything to provide the installation with a new MET clamped to the lead sheath since first thing I did was measure 8 Ohms Ze. (There was no MET, and a teeny single strand Cu wire earthing conductor wrapped round the sheath and probably corroded) - Now a better figure Ze (0.33) from which to begin.

I was very surprised that DNO guy said they have changed their policy recently, and now they won't replace break-outs like this even if they are 80 years old.

But what type of fuse do I record? (For supply protective device in EIC) ? I could just put "semi-enclosed fuse", 60A (TBC after inspection), and assume 1KA rated short circuit capacity. - Would that be reasonable?
 
Last edited:
It's still classed as BS 3036 protection, as are all rewireable fuses.... By the way the arrangement shown in your photo say's it's TN-S not TNC-S...

The DNO shouldn't of been happy with this service cut-out, in fact they have been instructed to replace all such iron clad rewireable service heads nationwide by 2011, which they haven't complied with.
 
Last edited by a moderator:
To be honest I don't think there is a lot more you can really do, but cater for worse case here. Your take on it being S1A and 1Ka is pretty fair.

Not sure what you mean by it being an TNC? it is either a TN-C-S or a TN-S and by the looks of things it is certainly not a TN-C-S. What was your Ze reading by the way?
 
What was your Ze reading by the way?


Stated in the OP's post mate!! lol!!

first thing I did was measure 8 Ohms Ze. (There was no MET, and a teeny single strand Cu wire earthing conductor wrapped round the sheath and probably corroded) - Now a better figure Ze (0.33) from which to begin.


Yep, first thing you need to do on your next visit home, is a trip to SpecSavers!! lol!!
 
ooops typo guys sorry I did mean TNS when I wrote it. Corrected now to save future confusions..

Thanks for the comments.

It's interesting to hear from Engineer 54:


The DNO shouldn't of been happy with this service cut-out, in fact they have been instructed to replace all such iron clad rewireable service heads nationwide by 2011, which they haven't complied with.
 
ooops typo guys sorry I did mean TNS when I wrote it. Corrected now to save future confusions..

Thanks for the comments.

It's interesting to hear from Engineer 54:

Too late I'm afraid
I have had to meticulously read each sentence to find the offending words and failed but all has now been revealed lol
 
pre-empted by ezzz. was going to say that i once had a fuse like that and called it albert, just because it looked victorian.
 
I am happy to don my big yellow gloves and pull a fuse but I personally would leave that, I'd worry it would break in my hand. I'd be much happier if it was changed, are you sure you cant smell what you think is burning lol, and while they are there...
 
Hi Shocking:


ring up DNO. they will get the head changed pretty quickly free of charge.
and they usually will convert to TNC.

Read more: http://www.electriciansforums.net/e...8154-what-do-you-call-fuse.html#ixzz2DWeGYIPN


Actually no because that's what I did do to get a MET (which wasn't 8 ohms!) and to ask for a new head. When the guy came round, he said they don't change these any more despite the age. He clamped on a new earthing conductor to the lead cable and left me to it.

I guess if customer was to go for a supply upgrade than they would do so, but probably unwilling to pay.

Actually it can be sealed with a wire (ring at top) but it's hardly IP4x though!
 
Hi Shocking:





Actually no because that's what I did do to get a MET (which wasn't 8 ohms!) and to ask for a new head. When the guy came round, he said they don't change these any more despite the age. He clamped on a new earthing conductor to the lead cable and left me to it.

I guess if customer was to go for a supply upgrade than they would do so, but probably unwilling to pay.

Actually it can be sealed with a wire (ring at top) but it's hardly IP4x though!


Get in touch with ofgem (or whatever the regulating body is called) and complain, that you have asked for this unit to be replaced and told by your DNO that they no-longer change these old iron clad porcelain rewirable fuse cut-outs.

These old iron clad with porcelain rewireable fuses have been deemed too dangerous for continued maintenance, (Health & Safety ruling) and as such had an undertaking from the DNO's to replace all these cut-outs by 2011, which they still haven't fully complied with. And no, it's not customer chargable upgrade
 

Reply to what do you call this fuse? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
I might be overlooking something that's right under my nose but opinions would be much appreciated. I visited a customer today with a detached...
Replies
25
Views
3K
Folks, Called out to a semi-detatched rental property today...TT, semi-enclosed wired fuse board, 4-way with a 500mA Earth Leakage Voltage main...
Replies
4
Views
2K
My customer needs bigger than 60A supply. Currently BS1361 60A. 4 bedroom house, 4 kids, new circuits.. Before I started in the place it came up...
Replies
38
Views
6K
Knobhead
K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock