evening gents,

bit of a sticky one that i would like some help on tonight,

called in by tiler fitting underfloor electric heating and asked to quote to provide power supply as far as the thermostat units.

The spec is as follows, two areas to be covered with seperate thermostat/control unit, 1st area 21m2 2nd area 18m2, total demand 200W per metre square, total maximum load 33A

Initially thought of spuring off ring but same ring in both areas on 32A breaker therefore no go,

only 1 spare way in CU available

both thermostats to be mounted adjacent to each other at border line between two heating areas.

no problem running 10mm t+e to where the controls are to be located but having a complete brain fart about how to split down to controllers and provide the necessary protection at that point? obviously SFU only good for upto 13A and one circuit is 19A
 
Have a read of the installation instructions. I have never installed a domestic U/F heating system that needs anything bigger than a 13a SFCU.

Cheers...........Howard
 
  • Like
Reactions: 1 person
Use 100 or 150 W /m2 matting instead or split each room down to two areas and use individual controllers for each area or install a contactor for each room that is operated their own controller. I think some need something extra if using contactors.
I would not like to see the electric bill for that!
and I hope they have a suitable supply to take the extra load.
 
Are you sure that your calcs are correct?

Unfortunately tiler hasnt purchased system yet has just quoted wattage figures from suppliers of 200W per metre square,

Yes the rooms are quite large 21m\2 and 18m\2 he is using 200w matting because of the size of the area that cant have UFH because of furniture etc.

May have to persuade him to split into 4 areas as this is the easiest
 
Just make sure that if he fits the UFH you test it before and after the tiles go down!
 
Just make sure that if he fits the UFH you test it before and after the tiles go down!

If i was signing of the job i would ensure full testing, however I am just providing the power supply, allegedly the supplier has an installation team it just seems that they cant cope with anything bigger than a bathroom thats only pulling a couple of As
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
wiring requirements for electric underfloor heating
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
james beckford,
Last reply from
james beckford,
Replies
7
Views
13,860

Advert