Discuss Large Volt Drop in ring circuit in the UK Electrical Forum area at ElectriciansForums.net
Andy
Hi Folks
This is my first post, but I've been reading many posts over the last few months and have found this forum very informative and some times very humorous, Thank you all.
I have recently come across a problem whilst doing some PAT testing for a customer that has left me confused. Although this is nothing to do with PAT testing it was my PAT testing meter that highlighted the problem when I plugged it into a socket.
The property is a 4 year old Timber barn and the loft has a small ring circuit with a spur off it feeding a socket below for a small telly.
My problem is that all of the sockets are only giving voltage readings of 60v but the reading for the circuit at the CU is the standard 240v
The only thing that I can think of is that when building the property someone has banged a nail through a cable somewhere.
I have been round all of the sockets and checked connections etc and found nothing obviously wrong.
When I mentioned it to the customer he said don't worry its probably been like it for ever and the sockets only supply low voltage stuff anyway.
Well I am concerned that its wrong and there is possibly a nightmare waiting to happen.
Im thinking of contacting the customer and trying to get him to let me rectify the problem
Is there anything else it could be?
I await your reply's with baited breath :)
need to know a lot more. are appliances plugged into these sockets working OK? what are the sockets used for? and more.
Appliances are plugged in and working. All low voltage stuff.
All voltages tested with a multimeter. Fluke 1653b
60 volts at each socket (thought i'd said that)
240 volts at CU for Circuit (thought i'd said that)
Could be looking at some Power supply 12/24VDC ,60V AC above earth ,and a very confused pat tester box.
(Customer says worry not )... but you know something is off !
Switch to DC , on anything apparently 0V !
Check appliances not 120V and you are seing some weird 60-0-60 Configuration .
I think SC asked what the 60Volts referred to L-N, N-E, L-E When you say all low voltage stuff, what exactly do you mean? the system you are working on 24o Volts IS LOW VOLTAGE.
I did indeed ask what the 60v was in respect to. If it's line/neutral, you could have a loose connection at the board. It's one thing sticking your probe (oooh err) in the MCB terminal screw and the neutral bar, but if it's loose, it's not going to help.
Thanks for your help guys but as I'm 2 hours drive away from the customer I'll sort it out myself when I'm back there and delve deeper when I can.
Toooo many questions and not a lot of help / suggestions
I was worried that this would happen as I've seen lots of times on here
Feels like I was back at collage
( Customer may be , vague if he knows of some 240-120 convertor box ...
wired inappropriately )
IEC cables to USA plugs should have been clue ... GONE !
If its wired weird , confirm a known good earth ref .
60V sounds planned .
And you still expect more help?
The questions you have been asked are relevant and will help with diagnosing the problem.
OP, unfortunately you're the one that's been to site and none of us (to my knowledge) are telepathic (although I am getting hints of beer and vino emanating from around Cheshire/Staffordshire and Northants for some reason) so it's natural we're going to ask questions to try and establish the fullest picture we can before dishing out advice, hence you see it happen a lot.
It's not meant to be a pop quiz, but your OP was a bit thin in terms of information especially regarding the measurements. 60v.... between where? (you've answered, stating between L-N and L-E), but when measured at the board (I'm assuming the neutral/earth bar and the MCB output terminal screwhead) you're getting 240v.
So if this was my problem, I'd be checking terminations and device connections in the CU. Especially as the issue appears to be affecting all sockets on the circuit... if it's a ring final circuit there is only one common place and that would be the CU, unless it's a lollipop, then there are two. If it's a radial, are the sockets the only thing on the circuit? If there is maybe a SFCU as the first connection, could be a loose connection in there which is having a knock on effect on the rest of them. But, as you can see, there are a lot of possibilities and so lots of questions.
Do you have other electrical test equipment (such as an earth fault loop impedance meter, low range continuity tester etc.) to test the circuit itself for other faults?
Where did that come from?
I am in Northants, I hasten to add not born in Northants and no devils juice has passed by lips:innocent:
I'm just about to have a sip or 6, like many I hate posts like this one, with very little information, with responses from lots of people only to be told, not much in the way of help was forth coming, as I get older (yes it was my birthday on Tuesday) I tend to get rather upset at some of the more, shall we say difficult posts to get any help from the poster, to that end I will not take part in any further discussion with regards to this post. Instead I will retire to the Drawing Room with her in doors, and continue to sip the red nectar.
A belated Happy Birthday Pete ;):)
Well belated birthday greetings :)
I shall be indulging in a beer or two later as compensation for coming home absolutely filthy three days in a row this week, so I shall raise a bottle or tinny to you :D
Your welcome buddy, enjoy your tipple. I'll have some later :).
As for the thread, I'm not even going to bother responding. My crystal ball is in for repair & the OP's attitude stinks.
Off to pick the kids up, catch you later.
Thanks for the info much appreciated.
You've confirmed my thoughts, so I'll be checking/testing everything on the circuit
The one place I couldn't get to for long was CU as we had to vacate the cabin as it had been booked out
As I keep saying the instrument I used for my testing wasn't the pat tester.
It was/is a Fluke Multimeter 1653b (does pretty much everything)
As I said to begin with its a sm Ring final circuit with 1 spur off.
I think that people have assumed I'm not qualified
You're welcome.
I didn't check the model number, but multimeter and multi-function tester are different things to me. One is what I use to test electrical installations and the other is what I use to do diagnostic work on electronic equipment. So I've (incorrectly) assumed 'multimeter' = 'multimeter' when in fact you're talking about an MFT. I'm not big on Fluke model numbers so it didn't click, hence my question about other test gear.
I re-read your OP whilst writing my reply and I missed the part where you said it was a ring final, sorry. So yes, check at the start of the circuit for loose connections and work from there.
If the place isn't too old, do they have the EIC from the original installation? I'd be asking for that and check some of the readings for the circuit against what's down on the cert. Could be a good indication of changes they haven't mentioned.
2 hours drive... hope you're charging them for that :)
Good luck and please come back and let us know what you find.
I apologise if you think my attitude stinks I never intend to upset people I just find it frustrating that I have to repeat stuff.
I also apologise for not having more information for everyone but it was a couple of weeks ago and its all I had and its been bugging me.
All I was really looking for was a couple of pointers I'd possibly not thought of.
Again please accept my apologies and I'll try harder next time.
You're welcome.
Sorry you are right I should have said Multifunction tester. My mistake.
Would be nice to be paid for the journey but it was quite a lot of work so I just charged all on a day rate (3 days). They've also asked me to do the electrics on a new very large cabin they are building in a few months (loads of work) :)
I will definitely let you know what I find.
happy belated birthday pete.
Reply to Large Volt Drop in ring circuit in the UK Electrical Forum area at ElectriciansForums.net
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...