Feb 29, 2020
457
97
103
Reading
Trainee Electrician
Maximum Earth Fault Loop Impedance for OverCurrent Device was calculated
230/(MCB Rating*5) * Rule of Thumb
is that correct?
And how are they worked out now after Amendment 3?
same as before but with a 5% reduction to allow for dupply voltage low limit of about 216V. think it's called a Ci factor.
Thanks ill try it but I just read on another forum
"The IET don't actually calculate it - it derives from the circuit breaker product standard."
----------/forums/forum/messageview.cfm?catid=205&threadid=39081
don't know if it's garbage?
[automerge]1583529462[/automerge]
Sorry it works perfectly, Thanks again.
------.org/forums/forum/messageview.cfm?catid=205&threadid=39081
WTF is That???
Reactions: Pete999
Yeah I found something on another forum and posted but after trying your suggestion and it worked I crossed out what I'd written before, Thanks.
thought i was going cross eyed and almost binned my Scotch.