You clearly have not produced anything to prove a tncs earth can not be exported
Ans you haven't proved that it can.
Discuss Exporting the earth? in the Electricians' Talk area at ElectriciansForums.net
You clearly have not produced anything to prove a tncs earth can not be exported
Ans you haven't proved that it can.
IQ and Lenny did. What more do you need?
Antimatter,
can I ask then, if you are installing outside lights or sockets wired to the main building which is on a TNCS....do you rod them individually,and separate the earth....or use the TNCS?....I ask because logically if you are so appalled by the thought of a shed on a TNCS then presumably you feel the same about an outside light?.....if not why not?
The best example is the outside socket, used exclusively in the main for garden tools and the like.... If there is a possibility of RISK, then surely this is the best example of how ludicrous some of these objections are!!!
Outside light has the CPC connected to the MET, if extraneous metalwork in an outbuilding can introduce an earth potential within the installation.
I think you are a wind-up, either that or you haven't bothered to read any of the posts that don't agree with your very confused version of the Reg's, ....or come to that ''common sense''
ah the old lost supply neutral again. common as rocking horse s++t. happens every day.
Straight from the IET FORUM
The inspector has asked for a metal shipping container cabin housing a db for a soil washer to be made into a TT as the supply is a TNCS pme .Now i understand you cant export PME but the feed for this db comes from another metal cabinet which in turn is fed from a metal shed all pme .
so is this user on the IET forum wrong as well chaps? or do you want me to post more examples?
ah the old lost supply neutral again. common as rocking horse s++t. happens every day.
If you bothered to read the rest of the thread that you copied & pasted that post from, you would see that they infact agree that PME can be exported to an outbuilding!!!!!!!!!
If you bothered to read the rest of the thread that you copied & pasted that post from, you would see that they infact agree that PME can be exported to an outbuilding!!!!!!!!!
I can no longer deal with this......in the words of Peter Jones......I'm out.
Ahhhh, the sweet sounds of defeat, i knew i was right all along
Its true that persistence really does pay off
ONLY in your dreams antimatter; ....Only in your dreams!!!!! and you can take that to the bank!!! lol!!!
ah the old lost supply neutral again. common as rocking horse s++t. happens every day.
This situation could be very dangerous, because all earthed metalwork would be at 240 V above the potential of the general mass of earth.
Common - not, Dangerous - very.
Do you want to take that chance? its your name on the paperwork, not mine.
Which is why equipotential bonding is very important, providing the installation has an RCD and the above happens, and all equipotential bonding is in place and resistance is 1667ohms or lower the RCD will operate.
Every time I read of the mass deaths from broken supply neutrals on exported TN-C-S system, I will think of you.
You should contact BBC Watchdog with your findings, you are a national hero of electrical engineering and I am turning to landscape gardening to contemplate my ignorance.
Ahhhh, the sweet sounds of defeat, i knew i was right all along
Its true that persistence really does pay off
antimatter shhhhhhhhhhhhhhhhhhhhhhhhh!
please respect your elders because the will now a hell of a lot more than you!!!
there is so many blokes on here just trying to help and from what i see all you want to do is cause problems!!!
danny
im not saying its a text book, all im saying is iv been on here and needed advice regarding all sorts and someone has help me, the people that have helped me you seem to be having a problem with. imo everyone has there own opinion which is fine but please respect the member on here!!!
danny
Because my interpretation of the regs is different from other peoples doesn't mean that im causing problems at all, on the contrary, it is others if you read the earlier posts who are derogatory to me, please read the posts back, this is a forum not a text book, and different people have different opinions danny
The problem was never about your opinion, as you say you are entitled to it. It was the fact that at the start of this thread you told the op that they can not export a tncs earth. You did not state this as your opinion, you stated it as fact. Which it is not.