Found it,
Where PME conditions apply
3.1 Cable conductor overheating
Where PME conditions apply
* , the use of the armouring of a cable as a main bonding conductor may result in overheating of the live conductors where they are to be operated at a significant proportion of their current-carrying capacity for sustained periods or at higher ambient temperatures. ‘Overheating’ of a live conductor, in this context, is where the conductor operating temperature exceeds the rated value appropriate to the insulation material (such as 70 °C for thermoplastic (general purpose pvc)), which can lead to premature ageing and deterioration the insulation.
Such overheating is related to the diverted neutral (or network circulating) currents which the main bonding conductors of a PME supplied installation may have to carry for sustained periods under certain conditions. Part of the I2R heating produced in armouring, when it carries diverted neutral current, is transmitted to the live conductors of the cable, which can result in their overheating.
The probability of the live conductors of a cable overheating due to diverted neutral current in the armouring, such that consequent premature ageing of the insulation is likely, is reduced in the following two cases.
• Where the cable is lightly loaded (bearing in mind that the heat produced in a conductor is proportional to the current squared) and the ambient temperature is in the normal range expected for occupied areas.• Where it is expected that the armouring will not carry a significant magnitude of diverted neutral current. (That is, where none of the extraneous-conductive-parts which the armouring connects to the main earthing terminal are in contact with the general mass of Earth or may reasonably be expected to come into such contact).