Discuss 100+ volts down earth ???? in the UK Electrical Forum area at ElectriciansForums.net
JD6400
Mentor
Just had a call from two of our men who are testing an agricultural dealership , they have found 100 + volts on one of the lighting cpc's .
To cut a long story short , they have cut around 2 and a half meters out of the 10 meter the circuit ( 1.5 T+E ) and have it laid on the floor . They say that they are getting +500 between all conductors ( Two different Fluke MFT's ) , but when they put power on it ( without connecting the cpc either end , they are still getting 100 + volts on it !
Any thoughts !????
Any thoughts !????
Is the cpc connected to the MET? Have they done a R1 + R2 test? It sounds like a induction/eddy current if there is a break in the cpc. Find the break in the cpc re connect it and the 100+ volts should go away!
Yeah sounds like a coupled or induced voltage. Use an analogue voltmeter for exactly the same test and it will probably show 0v.
Induction voltages are more common in systems wired in singles ie cpc with phase and no neutrals to cancel out phase induction. However they can occur in systems wired I. Twin & earth my guess is that the induction voltage is carried across on the switch wires (again no neutrals). If an induction voltage is carried across to the cpc it goes away when the cpc is connected to the MET. I don't know why though I'm not that clever!
At the moment it is a 2.5m length of T+E laid on the floor ( cut out of the circuit ) , with live and neutral connected but not the earth . All conductors have megged out at +500 on two separate Flukes , but they are still getting over 100 v on the earth conductor ?
I have since spoken to them again , and they say that it appears to be the same on other lighting circuits as well .
They are bringing it back to the stores , and I will check it out next Tuesday when I am back down the yard again .
Thanks for the reply anyway .
If they've meggered the three conductors and all was okay then it has to be an induced voltage onto the CPC which is not connected therefor it's floating. If they're worried about it then connect the CPC so it's at earth potential and check the leakage current with an earth leakage clamp meter. Otherwise save a lot of messing about and try the original test with an analogue tester as I previously suggested.
Nice to see i'm not the only 1 that still uses an Analogue meter
I'm beginning to think they should only allow sparkies to use analogue testers for the first few years when hopefully they're experienced enough to know the importance of an instruments input impedance and how it affects the results it's going to give on certain tests ;).
Not trying to teach granny to suck eggs, but yet certainly sounds like induced voltages. Have they checked Earth continuity on the lighting circuits ?
Whats a analogue meter? Lol
Serious??? Analogue is analogue as it's name suggests, it has a moving coil inside and a needle. Digital is...well it's just digital with a digital display.
Analogue
Digital.
I hear what you all are saying and appreciate the input , but it is on a 2.5m length of cable .
Would that be long enough for this to happen ?
I have to admit that they did , and as expected it did disappear .
But it apparently created quite a spark on the whole circuit .
I originally suggested that they have a fair few fluorescents in the place , but none were on at the time .
It is the first time I have come across this on such a scale and especially on such a short length of cable .
Reply to 100+ volts down earth ???? in the UK Electrical Forum area at ElectriciansForums.net
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
5K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...