M

MHK

Howdy

I've come accross a situation where 16A MCB have been specified for ring circuits. The rings serve socket outlets having looked through the regulations I have been unable to locate any specific requirement stating that they can not be used, however, I would be grateful for some alternative views!

Many thanks in advance :-)
 
Why can't you use 16A MCB's? What size of cable has been specified? Sounds to me like a typing error.
 
The query wasn't necessarily as to whether you can or can't use 16A rings. There are approximately 200 ring circuits specified on 4.0 XLPE/LSF singles protected by 16A MCB breakers. I could understand if the intention was to reduce cable sizes by reducing the breaking capacity, however, this is not the case. I can really understand the benefit of wiring in this way?
 
Nothing wrong with using 16A ocpd for a ring final & you'll not find anything in the regs that says otherwise.
How big/long are the rings & what is the customer use.
 
The most likely reasons for the specification of 4mm[SUP]2[/SUP] XLPE (90 degree C operating temperature) and 16A MCB is this cable and it's protective device has been downrated because the cable is run through significant amounts of thermal insulation and/or areas of high ambient temperature and/or large number of cables grouped together.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
16A MCB for a Ring Main
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
MHK,
Last reply from
MarkieSparkie,
Replies
4
Views
24,444

Advert