Hello,
I was checking my breaker box during the process of shutting down my pool for the season. My pool equipment (pumps, timer) run at 240v. When I went to turn off the breaker, I realized it was two single pole breakers that were independent. That is, there was no handle tie so they could trip independently.

They are breakers 27 and 29, both are single pole 15amp Square D QO.

If I trip both, my voltmeter at the pump reads 0v. If I turn on either 27 or 29 alone, they read ~5v. If I turn on both 27 & 29, I get the expected 240-250v.

Two questions:
1) Shouldn't there be a handle tie between 27 & 29, or a double pole breaker?
2) Why do I see 5v when only one breaker is active? I was expecting 120v.

I did not install these breakers - we are fairly new to the house so the system predated us. But I'm puzzled by the setup.
 
What are you saying?....that it should be double pole and switching neutral as well as live?

It sounds like a 3 phase board (27 and 29) , in which case you are talking 400volts.
Getting on a bit, too (15 amp).

Photos and a decent explanation would help.
 
OP is in the US. With either breaker on, you would see 120V from hot to both neutral and ground, but no significant voltage from one hot to the other since the circuit is interrupted by the other breaker. The small voltage you are reading results from capacitive leakage to ground from whichever hot wire is not energised, which allows a tiny current to flow through the input of your meter amd give a slight indication.

Yes the breakers should be linked so that the circuit is not left energised from one hot while appearing to be dead.
 
OP is in the US. With either breaker on, you would see 120V from hot to both neutral and ground, but no significant voltage from one hot to the other since the circuit is interrupted by the other breaker. The small voltage you are reading results from capacitive leakage to ground from whichever hot wire is not energised.
Just realized, never looked just baffled.
 
OP is in the US. With either breaker on, you would see 120V from hot to both neutral and ground, but no significant voltage from one hot to the other since the circuit is interrupted by the other breaker. The small voltage you are reading results from capacitive leakage to ground from whichever hot wire is not energised, which allows a tiny current to flow through the input of your meter amd give a slight indication.
Got it, thanks!
 
Hello,
I was checking my breaker box during the process of shutting down my pool for the season. My pool equipment (pumps, timer) run at 240v. When I went to turn off the breaker, I realized it was two single pole breakers that were independent. That is, there was no handle tie so they could trip independently.

They are breakers 27 and 29, both are single pole 15amp Square D QO.

If I trip both, my voltmeter at the pump reads 0v. If I turn on either 27 or 29 alone, they read ~5v. If I turn on both 27 & 29, I get the expected 240-250v.

Two questions:
1) Shouldn't there be a handle tie between 27 & 29, or a double pole breaker?
2) Why do I see 5v when only one breaker is active? I was expecting 120v.

I did not install these breakers - we are fairly new to the house so the system predated us. But I'm puzzled by the setup.
My friend you need to go to Home Depot or Lowe’s and buy a 20 amp double pole GFCI breaker. All pool pumps and receptacles need to be GFCI breakers
 

Reply to 2 single-pole breakers (untied) for 240vac circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
842
Hello, I had an electrician install a 100Amp subpanel which feeds a mini split. I addition I added a Homeline 50A GFCI breaker to power a shed. I...
Replies
9
Views
2K
Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
477
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi guys , Happy 4th I had a 15 amp breaker trip in my panel when my mother was running her sewing machine. She flipped the breaker back but later...
Replies
0
Views
641

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock