Got a ceramic electrical hob with 4 rings. All add up to 6kw. The only instructions for installation are

"For UK only
A Switched Fused Connection Unit to BS 1363 Part 4 is
recommended.
The fuse must be rated at 32 Amps"



Is there something I'm missing but surely the hob should be wired in at least 4 mm flex as 2.5 flex can only take 25 amp.

Of course after demand taken into account people usually only use 2 rings and nobody in the right might would wire it into what the instructions are saying as it would burn. I've told the landlord pretty much can't install the hob on a 32 must be a 20 but it would probably trip if they use the 4 rings.

Also cant wire 4 or 6 into the hob as it won't fit

Any opinions what you would do ?
 
Will 4.0mm² 3183TQ Butyl Flex Black fit? - at least it is round, rather than oval shaped.
Nominal O.D - 13.1mm

[Edit: PS: I didn't put in the links to Amazon!]
 
Last edited:
That's what I'm saying lol this is their recommendation


"For UK only
A Switched Fused Connection Unit to BS 1363 Part 4 is
recommended.
The fuse must be rated at 32 Amps"
 
The 4 mm would fit also but 1. Surely it shouldn't be sold with the 2.5mm and also the 4 mm will fit but the cord grip won't fit over the cable
 
The 4 mm would fit also but 1. Surely it shouldn't be sold with the 2.5mm and also the 4 mm will fit but the cord grip won't fit over the cable

Not sure what you mean about the 2.5mm, if you are referring to the Amazon links that some overzealous software has added to my post, please ignore those, you can buy the cable e.g. from TLC. Perhaps just change the cord grip or make your own.
 
If the 2.5mm is attached to the unit as it comes out of the box - just use it


Fit to what. The manufactorer recommends fitting to a fused spur which is only rated at 13 amp with a fused rated at 32 which I'm pretty sure you can't get and then 2 5mm which is only rated at 25 amp. So would fit to the 32amp which wouldn't protect it or the 20 amp which would trip it ? ???
 
Fit to what. The manufactorer recommends fitting to a fused spur which is only rated at 13 amp with a fused rated at 32 which I'm pretty sure you can't get and then 2 5mm which is only rated at 25 amp. So would fit to the 32amp which wouldn't protect it or the 20 amp which would trip it ? ???

Find a local electrician matey.
 
There's alot of assumption in the thread for us to relpy to so can we first of all get the make and model of the hob or a link to the online installation guide.

You say its a 2.5mm flex, does it say this on the flex or are you guessing?
You claim the flex is 25amp rated - have you got this info from the cable manufacturers?
Would this hob be sourced originally from china or similar as their attempts to translate often don't tally well with actual English - I've just fitted a sump pump that must comply to 18th edition and claimed it was 3ph on the rating plate but comes with a 13amp plug top on it... If you have any issues with incorrect instructions you need to contact your supplier and let them do all the donkey work unless you are competent enough to realise the actual requirements and demand of the hob yourself.
 

Reply to 6 kw electrical hob with 2.5mm flex in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I've just tried wiring an indesit IB65B60 induction hob. I read the instruction manual and it said for 240v connections to put the...
Replies
23
Views
4K
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
Can I please check my understanding on the following. My ring is wired in 2.5mm T&E. It is on a 32 amp MCB and protected by an RCD. I am now...
Replies
12
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
772

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock