Discuss 9.5kw without DNO in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
H
hanky-pankysex
Can a 9.5Kw system be installed, commissioned and signed off without DNO notification and then notifying them or would gemserve or the supplier pick it up, if so whats the worst case scenario rather than waiting weeks?
If it is over 3 phases, then no problem.
If not, then don't do it. Worst case scenario? They find out about it and refuse your connection. And you'll have very little chance of getting a G59 install approved by them again.
G83 is for systems upto 16A per phase so a 9.5kWp system can be installed under G83 as long as you have used a 3 phase inverter or 3 seperate single phase inverters. So prior notification is not required.
Tom
the inverter need to be certified g83 compliant as well ! ( they would all pass its just a question of if your manufacturer did the paperwork as I understand it ) if not pm me we have in stock if you want to swap it out
Reply to 9.5kw without DNO in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Hello everyone, I currently have two solar modules left over from an installation and I would like to use them to set up a solar system on the...
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
4K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
4K