Hi,
I am fitting a new kitchen and would like to know if it's ok to connect switched 13amp FCU onto a radial circuit. The kitchen has a radial circuit with 4 x double sockets fitted - 2.5 twin and earth cable. I would like to add 4 x 13amp switched FCU's - one from each double socket so as I can plug in my appliances. Would this be ok/regulated to do?

Cheers

scot3
 
bear in mind that the total load of a 2.5mm radial is 27A (ref. method C). would it not be a good idea to convert to a ring, or fit a 2nd radial for your 4 appliances, maybe in 4mm?

edit: 27A is approx the load of 3 appliances ( like dishwashers) without allowing for diversity).
 
Hi,
I am fitting a new kitchen and would like to know if it's ok to connect switched 13amp FCU onto a radial circuit. The kitchen has a radial circuit with 4 x double sockets fitted - 2.5 twin and earth cable. I would like to add 4 x 13amp switched FCU's - one from each double socket so as I can plug in my appliances. Would this be ok/regulated to do?

Cheers

scot3
No not a very good idea. You will ideally need a new Ring Final Circuit ( RFC ) or a Radial circuit utilising 4mm2 cable, installed in your new kitchen to allow for heavier electrical loading's, Washing Machines, Driers, Dishwashers etc, to do what you suggest is far from the best option and you can't plug anything into a FCU it would need to be hard wired.
You need to get the opinion and experience of an Electrician to design a new circuit for you, it will need to be tested and certified anyway.
 
could be worse than DIY. he might get a kitchen fitter to do it.
 

Reply to adding fused FCU to radial circuit in kitchen in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
643
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
953
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
662
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619
Hi everyone. Im new here... I need advice on wether it is safe and okay to have 3 × 13amp fcus on its own radial with each having single socket...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock