1

1ManRiot

Bear with me on this one:
-Incoming DNO supply (3 phase) comes into a cabinet which is fed out to two distribution boards in separate (unmanned) buildings
-Our "customer" wants a cubicle next to this (there is no more room in existing one) with 2 isolators, one for each circuit, so they can isolate one building without going into the building and without isolating both together

My concern is that this separate unit isn't the main isolator and is before the DB protection/ADS, therefore not fault protected in itself.

Is this a legitimate setup, WRT 7671?
 
if i read you correct, all they want is an isolator for each CU. can't see a problem with that. all you are doing is interrupting the L and N to each CU. fault protection remains as it is now.
 
  • Like
Reactions: 1 person
Yeah that's right, it's just that they will be in a separate cubicle made me wonder if it was a legit way to do it, as normally they'd be directly alongside the cutout in an ideal world.
 
clear labelling on each CU, as in " isolator in cabinet X " would suffice.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Additional isolators in a separate cabinet
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
1ManRiot,
Last reply from
telectrix,
Replies
5
Views
998

Advert