Discuss Additional isolators in a separate cabinet in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

1

1ManRiot

Bear with me on this one:
-Incoming DNO supply (3 phase) comes into a cabinet which is fed out to two distribution boards in separate (unmanned) buildings
-Our "customer" wants a cubicle next to this (there is no more room in existing one) with 2 isolators, one for each circuit, so they can isolate one building without going into the building and without isolating both together

My concern is that this separate unit isn't the main isolator and is before the DB protection/ADS, therefore not fault protected in itself.

Is this a legitimate setup, WRT 7671?
 
if i read you correct, all they want is an isolator for each CU. can't see a problem with that. all you are doing is interrupting the L and N to each CU. fault protection remains as it is now.
 
Yeah that's right, it's just that they will be in a separate cubicle made me wonder if it was a legit way to do it, as normally they'd be directly alongside the cutout in an ideal world.
 
clear labelling on each CU, as in " isolator in cabinet X " would suffice.
 

Reply to Additional isolators in a separate cabinet in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Looking for a little advice and also hopefully some education :) Have recently bought a flat (for which warranty period has expired) which has...
Replies
0
Views
3K
Hi Have done some additions to an existing multibuilding non domestic site. I noticed no SPD on the mains intake side, they are in a reasonably...
Replies
13
Views
2K
Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
21
Views
9K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock