Hi,

New to the forum, but an experienced electrical DYIer. Decades of work on cars, also, house electrics, model railroad automation and arduino monitoring.

My reason for joining though, is really to get some advice regarding a quote I have received to get a property EICR compliant. The property is a '70s, smallish three bedroom semi-detached house with a garage.

I have been quoted a staggering £2140 for what appears to be relatively straight forward work.

- Supply and fit 10 way consumer unit with RCBOs
- Drill out back of kitchen unit to reveal water earth bond
- Change sleeving on immersion heater spur
- Change cable to immersion heater
- Fit screw to immersion heater cap
- Supply and fit 20 fire rated downlights
- Correctly terminate wiring for downlights
- Supply and fit rubber grommets to all back boxes
- Fit stuffing glands to garage sockets
- Remove rewirable fuseboard in garage and replace with fused spur
- Replace wiring between garage switches
- Replace non-working immersion heater boost switch
- Remove ceiling fan bracket and fit pendant cover in front bedroom
- Supply 5 year Electrical Installation Certificate

Most of these I could do in a day myself. If I add up items needed, consumer unit, RCBOs, downlighters, maybe I can see £400-450 in that. That leaves £1700 for the actual work to carry out. Even at £250/day, that's 7 days work.

Am I missing something obviously expensive in that list?

"Drill out back of kitchen unit to reveal water earth bond" - Is that just for inspection?
"Correctly terminate wiring for downlights" - what is actually needed here?

Hope for some guidance here.

Thanks
No harm to you but there's well, well over a day's work in that.
 
  • Agree
Reactions: Baddegg
I don't have any grommets in my backboxes.
My question is:
What reg states this about the backboxes having grommets?
Arguably 522.8.11 “Cable supports and enclosures shall not have sharp edges liable to damage the wiring system”

But like you say, if the cables are plastered in they’re not going to move so is the sharp edge liable to damage the wiring system other than during installation? Probably not.

For what it’s worth Codebreakers doesn’t mention grommets specifically. The closest you’ll get is probably un-bushed cable entry (sheathed cables) which gets a C3 if there are no signs of mechanical strain or damage, a C2 if there are and a C1 for access to live parts.

Again you could argue a C3 for equipment inappropriately installed but unlikely to lead to potential danger (134.1.1), but really that’s about it I think.
 
What mechanical damage mate? They are plastered into a wall and are not moving. No damage to the sheath unless the things are moving.
The reg mentions protection during installation as well. So as the spreader spreads his muck, he may inflict damage. It's up to the judgement of the inspector on whether to code it or not.
And some metal boxes are not bedded in plaster, being fixed to a wooden noggin with plenty of free movement of the cables. And if the sheath doesn't fully enter the box that's got very little protection. I've seen it many times. Only last week I had a cooker tripping the RCD, traced it to a neutral core chafing against the ungrommetted (made up word) back box.
 
I have been quoted a staggering £2140 for what appears to be relatively straight forward work.
Hi - as you have concerns about your quote then perhaps you just need some more quotes? I find that the more specific you can be the more likely you will get a quote that reflects what you actually want. Perhaps spend some time researching what down lights you would like installed, for example. Likewise with CUs, there is a significant variation in material costs with included functionality.
 
The price quoted for the volume of work is as others said - reasonable.
Not sure all items are necessary though for a satisfactory EICR;
Replace Consumer Unit - Reasons/RCD protection? Category?
Replace cable between switches in garage - why?
Install grommets to back boxes - C3!
Change sleeving on immersion heater spur - ?? BPG4 pg17 (Does not require reporting)
Change cable to immersion heater - Why?
Supply and fit 20 fire rated downlights - Non fire rated C3 at best unless something not telling us!
Correctly terminate wiring for downlights ) - Could be just connector blocks??
Fit stuffing glands to garage sockets - Why, Abrasion/IP issue?
Remove rewirable fuseboard in garage and replace with fused spur - Not necessarily a C2?
Replace non-working immersion heater boost switch - Not necessarily an EICR issue.
Remove ceiling fan bracket and fit pendant cover in front bedroom - More info req'd /C3
Supply 5 year Electrical Installation Certificate - 'Maximum' recommended interval is 5 years but the inspector could for various reasons recommend 1 or 3 years for example!
 
  • Like
Reactions: Baddegg

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice on electrical quote
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
morsing,
Last reply from
DefyG,
Replies
24
Views
3,034

Advert