Discuss Any IEE ISSUES WITH THIS INSTALLATION in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Scope of work . Run 2 x 2 core 1.5mm micc (pyro) from house CU to garage CU underground for apps 8 metres actually under some paving flags
PME incoming supply no water or metalwork in garage
20 amp rcbo protection at house CU
100 amp dp isolator in garage and two circuits 1 x 5amp for lighting 1 x 16a feeding 16 amp outside socket for car charging
been retired for a year so thought I would get a second opinion
 
I’ve had fun with pyro in a couple of churches and I’m not that old!
My more philosophical question is if you take a plain and simple 16A socket and decide to plug an EV into it does it, or does it not become mode 1 charging under section 722, and the delightful 722.411.4.1 then applies?
1626717243617.png

Or is that just too far fetched?
 
I'll swap ya for some 6mm² 3-core SWA. My world is too full of SWA and not full enough of MICC.

You won't get selectivity between the 16 and 20A OCPDs. Do you want the residual protection in the house or the garage. And, yes, earthing choices, choices...
 
Regarding the earthing issue what is the best practice then for car charging point
I hated to open that can of worms - but I think strictly speaking if the 16A socket is used for car charging then by rights you should select one of the installation methods in section 722 (updated in amendment one). Your call!

I'd suggest the quickest overview is probably this video which I think is very well made (though other charger brands are available):


Amendment one is available here:
https://electrical.------.org/media/2422/bs-7671-2018_a1_2020-inc-corrigendum-may-2020_read-only.pdf
 

Reply to Any IEE ISSUES WITH THIS INSTALLATION in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
548

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock