GBDamo
The load current of the circuit should be unlikely to exceed for long periods the current carrying capacity of the cable (regulation 433.1.204). This can generally be achieved by:
(i).....
(ii) not supplying immersion heaters.....
(iii) connecting cookers, ovens, and hobs with a power exceeding 2kW on their own dedicated circuit.
Now a timer that supplies a 2kW immersion heater, programmed to come on for one hour in the early hours, has been fitted to a FCU that is spurred off a RFC.
Am I being unreasonable in insisting a new circuit is run in for the immersion?
You are a more powerful electrician than me,I can only suggest to people what they should do,if I did insist my clients may tell me with words to the effect of "walk gingerly out of the door"
On a new installation,given the circumstances I would also be concerned about the rest of the installation
A fine tooth Comb may be required
Embarrassingly, this has been picked as a QS review issue, the insistence is for us to put this right.
The rest of the install was not done by us.
My own opinion is that an immersion on an RFC is OK if the immersion is only used as a back-up for the main DHW heating system (eg a boiler).
If it is the primary herating source then a separate circuit is needed.
The often misunderstood App 15 is informative and for guidance only. But some QS have their own particular bees in their bonnets, so you may have a hard time.
Reply to Appendix 15 (Informative) in the UK Electrical Forum area at ElectriciansForums.net
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
  • Locked
5K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
6K
In our house the main fuse is rated at 100A maximum. The individual circuits in the consumer unit, if all used simultanuously, add up to much...
13K