So, in response to the OP, the jury is out. As there is such a division of opinion I would say it's down to the individual installer and personally I wouldn't say it leaves your installation potentially unsafe.
 
Moggy, the purpose of bonding the array is nothing to do with the leakage of DC current onto the AC side of the installation - and I'm absolutely baffled by your assessor's suggestion that bonding is for lightning protection.
 
earthing, not bonding
I was a bit baffled as well.
my understanding is it's to provide earthing should the array become live due to leakage currents crossing onto the DC side, sorry, have ammended my previous
 
My reasoning for bonding the array frame with a transformerless inverter is simple: the DTI guide says I should and MIS3002 says I should do what the DTI guide tells me to. So, whether I agree with it or not, I do it. I couldn't care less what a scheme assessor or some monkey employed by an inverter manufacturer says because MIS3002 doesn't say I have to. Do you really think your scheme assessor knows more about PV installations than you do?
 
earthing, not bonding
I was a bit baffled as well.
my understanding is it's to provide earthing should the array become live due to leakage currents crossing onto the DC side, sorry, have ammended my previous

But surely the Dti guide is referring to bonding?

The framework and panels should all be class II so earthing doesn't come into it.
 
Are you bonding areas of equal potential though, or are you providing a path to earth for rogue current?
I think probably this has all been debated ad infinitum elsewhere, mostly by people far more knowledgable than me. so I can't see anything to be gained by going over it again TBH so I'll leave it there.
 
Are you bonding areas of equal potential though, or are you providing a path to earth for rogue current?

I'd say a path to earth due to the topography of the inverter. I see this more as bonding rather than earthing as we are limiting touch voltage rather than limiting fault time.

I think probably this has all been debated ad infinitum elsewhere, mostly by people far more knowledgable than me. so I can't see anything to be gained by going over it again TBH so I'll leave it there.

Likewise and agreed!
 
I kind of thought I may get a 50/50 response.

Here's what I got.from SMA. (Now do I believe the SMA monkey, I have 2 arrays maybe bond one of them LOL. Kidding)


"The event 601 is as you describe, DC Grid feed in.

This can be caused by a number of things, certainly in the first instance, I would suggest that you check with your installers to check that your array has been correctly bonded to earth, they should be able to sourse the correct bonding information from the manufacturer of the array frame.

The 10223 event number ist he inverter saying that it cannot find a power reducer box, so the time interval for checking has expired. The power reducer box is not used in the UK, so this is of no concern for us here.

Best Regards,

Darren.

Von: [email protected]"
 
Thanks for all your responses.

Hypothetical question.

If one of your customers came to you with the above error and that response from SMA what would you do?
 
is it correctly set up for the UK?
I can't see DC grid feed in being anything to do with bonding/earthing!
 
Last edited by a moderator:
yes, but I can't see that being associated with bonding.
According to my assessor who took me to task about this, G83 doesn't necessarilly mean it's UK set. How long does it take to power up, should be 3 minutes.
 
That's interesting. Some other tiny countries might jump on our bandwagon and use G83, but otherwise I would have said it is very much a UK standard.

3 minutes is after a grid failure. When first starting up from cold the 3 minutes limit does not apply.
 
Don't bond the array to the MET!! Your all electricians here and there is no need to bond anything that is not a parallel path.
Test it to see!!
All that will be achieved by bonding it, is creating a form of lightning conductor!!......
Supplementary bonding may be required, again testing can prove this. Or if manufacturers state sup. bonding these must be followed.
But definitely do not earth it to the ground!! You will introduce a difference in potential that could and will be potentially life threatening.
It's not rocket science just basic electrical theory. It's all in bs7671
 

Reply to Array bonding needed? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
458
I quite often contribute on other's posts about issues with RCD's, thought I'd tell you about what happened to me yesterday as a little bit of a...
Replies
3
Views
2K
I had been sent on the NIC Solar PV course last year to learn how to test the DC side of solar installations as my company are testing solar...
Replies
5
Views
2K
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K
Hi Everyone, I'm new to this forum and am hoping someone can give me some advice, as I'm absolutely clueless when it comes to these things. I'm...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock