I think in general I'm largely in agreement with you, Malc.

Unfortunately, with regards to this issue PV installers must go by the decision tree - whether they like it or not.

As for bonding and earthing, I know what you mean. The Dti guide itself refers to it as both bonding and earthing in different instances which confuses people even further. Bonding IS, for reasons that escape me, badly misunderstood.

Well mate that just about sums it all up .................. we have a guide written by the looks of things by civil servants and not a technical input in sight.

Bonding in misunderstood because the training these guys receives is pitiful. We are no longer training guys to teach them an industry, but to pass exams and assessments so that they can stumble along in the industry and hopefully not kill or injure someone.

I sometimes wished we had more incidents in our industry, a few more deaths or a few more properties burnt down, may just may convince the bureaucrats that what they are doing to it is criminal. Yes domestic is not rocket science a few cable pulled in here and a few bits and bobs and there you go, bit like a nurse or a doctor taking your blood pressure, whack on a cuff, read a screen and there you go .....high blood pressure, but isn't it wonderful that that doctor will know why it's high, and what he can do to decrease it, that is called training, we just have guys that know yes wire A goes into equipment B not not a clue why
 
I could not agree more with Malcolm, I am not a sparky, but my background is more mechanical, if you get an electrical problem on a car, it is far more complex, 108 tiny wires to an ECU and you have to find the fault, so you have to understand how it works, to then work out why it does not.
It is sad that I appear to have a better understanding of PV systems than some sparky's (only some), and they are installing it.
The bureaucrats do seem to believe that if you can fill in reams of paper work, then the customer will get a quality install, I am waiting for the sad day when someone does get hurt.
 
I don't think the people you talk of earthstore are actually electricians.... Else they could work out what is right and what is wrong.
Ok yes, training they receive is a big factor, but as a professional should it not be on your shoulders to ensure the job you do is correct and up to current standards??
 
Thank you, Professional, I like that,
I do not install, I will help if need but only as an assistant, when I have sold a job, I kind of project manage it from beginning to end, I check that all work is to a high standard, from mounting of the panels through to the wiring, I work with the installers to make sure everything is right for the customer, so that I am proud of the work that I have sold.
I have learnt so much from this forum, as there are many experts here, so I am aware of how it should be done.
The PV industry has now got so complex, but I try my hardest to keep up with it all.
Pride is a word that appears to be lost in modern society, but some of us still have it.
 
strange how when managing projects it's the time served apprenrice trained electricians who have tried to insist everything has to go on an RCD under 17ed, and that it's fine for the PV to go on a shared RCD, and aren't prepared to listen to anyone telling them different. At least the short course guys tend to be willing to listen and learn, unlike the arrogance of some time served sparks.

Now, shall we stop making sweeping generalisations and chucking insults at people and get back to the topic.
 
What amazes me here is the complete lack of electrical knowledge in this

When I did my PV course and this came up, and the tutor said yes you bond back to the MET unless it is PM-E, which it wouldn't be, but I let it pass it is TNC-S in the installation, when it is TNC-S you stake it .................what!!!!

Why ........because the DTI say so....ahhhhhh so if you had a stainless steel boiler flue that could be touched while also touching the frame, that flue is obviously connected to the boiler, pipework is connected back to the MET via main equipotential bonding, and you then bond your frame to an earth stake ................how safe is that when you have 2 potentials within touching distance on the roof ...................blank stares we shall move on
tbf to the dti guide, this was a problem with your tutor, not the guide.

The guide says bond to MET if it's in the equipotential zone to avoid this issue.
 
strange how when managing projects it's the time served apprenrice trained electricians who have tried to insist everything has to go on an RCD under 17ed, and that it's fine for the PV to go on a shared RCD, and aren't prepared to listen to anyone telling them different. At least the short course guys tend to be willing to listen and learn, unlike the arrogance of some time served sparks.

Well you always get some. Tend to be the ones who hate updates and testing there own work as they know it's good LOL
 
TBH the whole issue of having to go to a spike if it's TNCS makes no sense to me, it's totally inconsistent to my mind. If we say an attached garaged is in the equipotential zone then why is a structure attached to the roof not? It's even acceptable to bond back to the MET on a detached garage according to ELECSA as long as it's not too far away (this was the scenario on my first assessment, they declined to say what 'not too far way' actually meant).
I can't really fathom why there is such an inconsitencey.
 
Last edited by a moderator:
You can extend a equip zone anywhere in theory. Aslong as you bond any services or parallel paths in that part back to the MET at the origin with a unbroken cable. I.e normal bonding rules. The only thing is you need to calculate the size of conductor required to stay under your 0.05 ohms.

As for bonding the array. I don't see that it should be introduced into the zone. As it is not in contact with the ground. So no parallel path. At all.

This reminds me of an example. Would you bond your knife and fork, there metal. And you can touch them and a bonded pipe..... LOL
 
I don't see why it should be either, but if it has to be I don't really see why it needs a spike on a TNCS when other things don't.

This reminds me of an example. Would you bond your knife and fork, there metal. And you can touch them and a bonded pipe..... LOL

I've seen door handles and bannister rails supplementary bonded!
 
Last edited by a moderator:
The stake on a tncs is an absolute no no. I'd never even contemplate it.
All you will do is cause a potential difference.

I seen this on a farm, well reversed.
Retarded spark put new cct on tncs. And the difference in potential between the farm (TT by requirement)
And the new cct. Killed cattle.
 
tbf to the dti guide, this was a problem with your tutor, not the guide.

The guide says bond to MET if it's in the equipotential zone to avoid this issue.

Are you a PV installer, becasue even though i'm not I still know that the current DTi guide tells you that if you have a TNC-S system that needs bonding it must be spiked ....................or am I wrong
 
All you will do is cause a potential difference.
potential difference to what though?

under the DTI guide 2006 decision tree the frame should only be bonded to a seperate earth spike in situations where there is nothing else for there to be a potential difference to. If there is anything within reach of the frame that was bonded to the MET then the frame would have to also be bonded to the MET.

That's the argument in favour of this as far as it goes, along with not unnecessarily bringing the equipotential zone out on to the roof (via bonding to the MET), as anyone then accessing the roof / frame via a metal ladder, or scaffolding and touching the frame would then introduce the danger of a potential to earth via the ladder / scaf that was different enough to that via the MET bonding to cause problems if both were touched at once (pretty likely).

Personally though we've not been installing earth spikes, or earthing the frame at all unless we actually measure a potential to earth from the frame since last Autumn when I realised that the new draft guidance matched our real world experience and measurements that show bonding the frame to not be necessary unless there already was a potential to earth.

Comparing the risks from the few micro-amps worth of leakage current the panels / frames may end up carrying with a TL inverter vs the risk from either earthing or bonding the frame resulting in a potential to earth that didn't exist before, and IMO the safest option is not to bond or earth the frame.

If there is potential to earth via the frame already, then that changes things.

The risk of a slight tingle from the frame in damp conditions can be entirely removed by switching the DC isolator off anyway before accessing the roof, which is the instruction we give to our customers.
 
Are you a PV installer, becasue even though i'm not I still know that the current DTi guide tells you that if you have a TNC-S system that needs bonding it must be spiked ....................or am I wrong
you're wrong.

In the equipotential Zone? >> Yes >> bond to MET*


if it's not in the equipotential zone, then you would bond to an earth spike if you were following the 2006 DTI guide.






*actually it calls it the consumer earthing terminal, but I take it you'd accept that this is what it means.
 
Last edited:
Are you still not following the 2006 guide, as the new guide is still under consultation I believe ..............or have you started working to it?

How is something on a roof in the equipotential zone, unless you extend the zone out to it which the 2006 guide tells you can't ?
 
Yes that makes sense. I can see that bonding it to the met in a TN system could introduce a potential to a metal ladder. Which as you said. Is exactly why it should not be bonded. At all unless you do somehow measure continuity from the frame to the met.
I think more people need to just stop for a second and think before just following these guides like yourself. It will make perfect sense to them if they think about it. And after all they are just guides.
 
Are you still not following the 2006 guide, as the new guide is still under consultation I believe ..............or have you started working to it?
mostly we are, but in this case no we're not because we believe it to be unsafe, and the draft guidance gave me sufficient support for what I was already thinking to take the decision to stop doing something that was unnecessary and potentially dangerous just because some 6 year old guidance written when TL inverters had only just hit the market said we should.

I'd be surprised if the authors of the 2006 DTI guide had installed anywhere near as many TL systems as we have, and our real world experience indicates that the issue they were trying to guard against is simply not a problem in reality.

How is something on a roof in the equipotential zone, unless you extend the zone out to it which the 2006 guide tells you can't ?
it's in the equipotential zone if some other bonded metal system is already bringing the equipotential zone on to the roof within reach of the frame (eg gas flue), or it's below a velux and within touching distance of a radiator etc. (or by some interpretations of it, just being within touching distance of a velux itself).
 
The velux??
That doesn't need bonding either.... Lol.
I can see your point about people hanging out the window and holding the rad for support. But like you said if the array isn't bonded then there's no chance of them coming to harm as it is on the roof with no path to earth.
 
So would I be right in saying that most think bonding isn't required but some are doing it because the current DTI decision tree says so?

Im not sure why SMA suggested getting the installer to make sure the array is bonded when I asked about the 601 error (unless they think a difference in potential somewhere would be detected as DC current by the inverter). I believe the arrays are not bonded.

Anyway the 601 events which happen approx twice a week up until now were before and after feed in. I now think this may be a coincidence as I was up and out earlier this week as I have been working away and there was a 601 error around the time I was getting ready (i left at 6am, a while before feed in).

The only things electrical I would have used would have been lighting. My suspects at the moment are.

Led lighting 6 x 3w mr11 running off 3 12v 1a DC psu (2 lamps on each psu)
Led lighting 5 x 6w mr16 GU10 240v

Illuminated Bathroom mirror 140w halogen with wound transformer (has a pull cord I need to replace as one set of contacts are going bad, pull cord is on the 12v ac side).
 
SMA recommend that solar panel rails are earthed when using SMA inverters without a transformer. i.e TL's.

Quote from an email received from Mark Ryder at SMA:

"SMA do suggest that you earth the solar panel rails when using inverters without a transformer.


Kind regards, Mark Ryder, SMA UK"


The Importance Of Earthing Solar Panels:

Earthing solar panel frames - Energy Matters

The reason to earth solar array frames installed with transformerless electronic

inverters, may be for functional operational reasons, not just for safety concerns.

I have seen evidence of a solar system with SMA 3000TL perform differently relative

to another local system, after it was earthed 10 days after installation.

Earthing the array frame changed its performance relative to another local system.
 
Last edited:
I had/have a DTI document which provides guidance and explanations to the content of v2 of the DTI PV guide. Unfortunately I can't find it at the moment (and may not have liberated it from my previous employer). It did go into the reasons why they required an array frame to be bonded if using a transformerless inverter. Bear with me on this as my memory is sketchy, but it was something to do with the simultaneous occurance of a fault on the inverter sending AC to the array and a fault with the array or DC wiring presenting AC to the array frame work, coupled with the likelihood of some chap up an aluminium ladder that is connected to earth touching said array frame. Don't quote me 100% on that but it was something equally as convoluted and unlikely.
 
well if that's the problem they're trying to solve, I'm not too concerned as I'd expect that sort of a fault to trip the RCD on the AC side 99.9% of the time, and we've been installing an individual RCD on each AC circuit on virtually every install we've done.

it'd also require multiple fairlures within the inverter, and the inverter remaining stuck on the on position - something I can't see happening for anything other than a lightening strike.

It's also solved by instructions to switch the ac and DC isolators off before going on the roof.
 
Spoke to someone who is influencial in the MCS arena and in conversation asked him about bonding of the array for TL inverters and he told me to read the new version of GN7. Yet to read it but lead to believe it states no need to bond.

He also when onto to say the DTI guide is 'guidance' only and then started on about lockable ac isolators, dc isolators when you've got integral isolators in the inverter and type A RCDs!

Apparently the new DTI guide will reveal all!
 
Spoke to someone who is influencial in the MCS arena and in conversation asked him about bonding of the array for TL inverters and he told me to read the new version of GN7. Yet to read it but lead to believe it states no need to bond.

He also when onto to say the DTI guide is 'guidance' only and then started on about lockable ac isolators, dc isolators when you've got integral isolators in the inverter and type A RCDs!

My point exactly. These publications are only guides. BS7671 holds all the answers for the requirements.
I don't see the need to bond them. Unless maybe they require a functional earth. This is earthing not bonding anyhow.
This would be to the MET and never to an electrode.
All the confusion seems to be caused by people listening and trusting too much to what there told and not checking for themselves.
Good to see everyone on here is trying to get this confusion sorted :)
 
It's mandatory to comply with all the double-ticked items in the DTI Guide in order to comply with MCS rules - or are MCS now saying that they can bend their own rules? Also the single-ticked items are mandatory unless you can show good reason for a variation.

This is all in MIS 3002 v2.1 para 4.2.

For the purposes of this standard, all double-ticked items in the DTI guide are mandatory. Compliance with all single ticked items is also expected unless reasonable justification can be given.

But having said that there are no ticks, single or double, against the tree diagram itself.
 
But having said that there are no ticks, single or double, against the tree diagram itself.
well if there's no ticks then there's no ticks.


also, if NAPIT send a sodding gas engineer out to assess us again, and try to get me to bond the frame to the MET on an SB1200 inverter with full galvonic isolation just because it's near a skylight.......:66:
 

Reply to Array bonding needed? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
529
I quite often contribute on other's posts about issues with RCD's, thought I'd tell you about what happened to me yesterday as a little bit of a...
Replies
3
Views
2K
I had been sent on the NIC Solar PV course last year to learn how to test the DC side of solar installations as my company are testing solar...
Replies
5
Views
2K
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K
Hi Everyone, I'm new to this forum and am hoping someone can give me some advice, as I'm absolutely clueless when it comes to these things. I'm...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock