Yes, quite right, he has done all he can do. I would have issued an advisory on the t&e our own document, BG may have such the same,?Assuming there is a 60amp fuse in the head then that 10mm t&e does not have overload or fault protection for the length of run.
The meter guys are there only to change the meter so they can not just disconnect a unsuitable cable just in case it feeds a freezer etc blah blah blah but they should of advised the client of the poor install (but at least he tried to double insulate)