Discuss Blowing sockets and popping RCD in the UK Electrical Forum area at ElectriciansForums.net

The problem was a debris in the terminals of the old sockets. a lot of plaster dust from the plasterer as they were doing the place up

That's surprising and I think there might be more to it than plaster dust itself. Dry / dusty plaster is a reasonable insulator. Wet plaster is conductive but one would have to form a bridge of wet plaster from the line terminal to the earth to get enough leakage to trip an RCD.

What were the IR readings before / after corrective action?
 
That's surprising and I think there might be more to it than plaster dust itself. Dry / dusty plaster is a reasonable insulator. Wet plaster is conductive but one would have to form a bridge of wet plaster from the line terminal to the earth to get enough leakage to trip an RCD.

What were the IR readings before / after corrective action?
Results were the same before and after 🤷‍♂️
L-N >999
N-E >999
L-E >999
 
Fare enough just not used to testing before carrying out work. Will think about this moving forward
It's good to hear you say that. If you start making this a habit then it will definitely save you a heap of hassle one day. As well as being required by regs (as @Lister1987 explained) checking things are fine while you still have the walk-away option is a fundamental self-preservation tactic!

By the way, I'm sure several of us could think back to our first post on here and shudder slightly! It's worth sticking around. There's lot's of great people lurking around willing to help.
 
It's good to hear you say that. If you start making this a habit then it will definitely save you a heap of hassle one day. As well as being required by regs (as @Lister1987 explained) checking things are fine while you still have the walk-away option is a fundamental self-preservation tactic!

By the way, I'm sure several of us could think back to our first post on here and shudder slightly! It's worth sticking around. There's lot's of great people lurking around willing to help.
Definitely đź‘Ť
 
By the way, I'm sure several of us could think back to our first post on here and shudder slightly! It's worth sticking around. There's lot's of great people lurking around willing to help.
I am sure if we are being honest, most of us will have a little shudder thinking back on some of the first jobs we did on site.
 
I am sure if we are being honest, most of us will have a little shudder thinking back on some of the first jobs we did on site.
I remember an under manager at our first wholesalers causing great amusement by taking me apart as an apprentice with a list of materials to pick up. I let it rest for a few years before ripping him apart on numerous occasions when materials I wanted weren't immediately at hand, faulty or just crap.
Standing joke, for a good while, how he used to make himself scarce before I got to his office.
Give him his due, though, he was always one of the first to offer me drinks when we went on various free do's.
He ended up very high up the supply chain and a very useful contact in the trade. They don't seem make 'em like that, these days.
 
It's good to hear you say that. If you start making this a habit then it will definitely save you a heap of hassle one day. As well as being required by regs (as @Lister1987 explained) checking things are fine while you still have the walk-away option is a fundamental self-preservation tactic!

By the way, I'm sure several of us could think back to our first post on here and shudder slightly! It's worth sticking around. There's lot's of great people lurking around willing to help.
I just started out in the electrical field and this thread has definitely taught me a lot.. never considered that testing had to be done before making alterations but it makes sense. Becoming good at testing will definitely prove useful in the long run.
 
No they were not reversed I checked my connections like I said. I also used my socket tester before I left which shows if all cables are in the correct terminals
I doubt your socket tester will see N - E reversal.

It could also in the right circumstances account for a light when switched on to trip a rcd.
 
Last edited:
Damn this is getting interesting, I'm waiting for his continuity, IR, Zs and RCD readings using the new x1 AC test now amendment 2 has been published. I also can't wait to find out if the 'client' gets his minor works cert. More importantly, did it get fixed and what the problem wasđź‘Ť
I didn't know that there is a new x1 AC RCD test ? How does that work compared to the old one ?.
 

Reply to Blowing sockets and popping RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
619
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
818
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
866
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
742
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
554

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock