Discuss Board Change, satsifactory report in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
G
graham123
Hi all, am going to be doing an inspection on a property which the customer wants a satisfactory report. ie no c1's, c2's. First question Bathroom lighting circut has no 30ma rcd protection, so a C2, next problem lighting circut into bathroom has no Cpc. Can i get around this by installing supplementary bonding in the bathroom?. What does no earth in lighting circuts go down as? C1?. I suspect the board my be a rewire able so possibility of a new board, but how can i give them a satisfactory report? my mind boggles. Thanks
The customer dictating how the report will come out? That's a good one. Your report will be what it will be mate, all you can do is code it up and quote for any remedials needed/recommended
Well no earthing in lighting circuits goes down as a c3 as long as no class 1 (metallic) fixtures are used and a suitable label fixed at the db. IMO if it has no earth and it has an enclosed ip rated fitting, it would not require supplementary bonding either, although I would wait for someone to confirm/diasagree with this, all other bathroom circuits would require 30ma protection or supplementary bonding.
If you fit a new board just fit an rcbo on the lighting, it will still give shock protection.
Depending in age of install I'd say both lack of RCD c3 and lack of cpc to lights c3, as long as no class 1 items and circuit is 2 core throughout. I would recommend to my clients RCD protection & lighting circuit rewire would be beneficial. Is bonding satisfatory ?
It sounds to me like a case of "You give me very nice report & later I give you very nice Balti"
Graham, have a read through the guide below, some of your code suggestions are rather strange and how would installing supplementary bonding allow you to 'get around' the lack of a CPC to a lighting circuit?
http://www.esc.org.uk/fileadmin/use...y/best_practice/BestPracticeGuide4-Locked.pdf
I was under the impression that if you had a lighting circuit which did have a cpc, then you could install supplementary bonding and you would not require rcd protection. But im not sure about lighting circuit with no cpc, is their no alternative to a rewire of that circuit?
Candles perhaps? :clown:
Why are we fitting supplementary bonding on a CU change ?
Does the "board change" in the thread title have no relevence ?
i seem lost on where this is going lol.
The title of the post is a bit confusing with the text saying your about to carry out a inspection!
Graham IMO I would carry out the PIR first and identify exactally what faults exist at the premises !
That is if it is a PIR your about to do!
you don't leave a classI fitting with no earth.
Reply to Board Change, satsifactory report in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
So I've recently had an EICR for my building. Came back with about 20 odd C2 remedials and a few F1's which resulted in UNSATISFACTORY being...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
hello all, pardon my ignorance in not employing an electrician, however, im a diy'er whos changing the light switches in my house and came across...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...