So theoretically speaking, hypothetically: if there was an incoming water pipe which was INSULATED and no gas pipe, and a PME/TN-C-S failed the metal accessories could become live and will not trip any protective device as there will be no active earthing system in place for the house?
The accessories will go to the PME potential in any case. If bonded to significant lengths of metal gas/water pipes that is probably fairly close to 0V (in the tens of volts range) but if insulated pipes then it goes to whatever the remaining N/E load might be, so conceivably to 230V if the fault is on the last TN-C leg to the property.

The lack of any trip is a problem, but in any case the external risk is independent of the RCD tripping as that only isolates the L & N and is not isolating the E.

However, the EV protection system do isolate all 3 so if a fault is detected the car is not left at a potentially dangerous voltage that someone might be washing, etc.
Now if you did TT the shed, then the sheds stuff (any tubs metal light fittings etc) will be earthed, BUT because the regs have said NOT to earth the armouring to the OUTBUILDING you are then lacking earthing in the MAIN building (house)... So shouldn't a TT earth ground rod be installed for the house too then or shouldn't they advise to connect the armouring/cpc to the outbuilding too as well as have a TT ground rod for the outbuilding?
If they are connected (and the house is not TT) then the outbuilding is not TT either, it is TN. The 2nd 'T' is the direct connection to the local Earth!

Some other countries require an earth rod for the house as well, in effect adding more "multiple earths" to the PME arrangement. The ROI is fairly close to the UK in many ways and does this, as does the USA and Australia. The 2nd amendment regs put up for discussion before Xmas look as if that will be added to the UK as well (at least new builds to provide an earth in the foundations).

Now the problem in reality is it is hard to get any sort of low impedance rod. Typically you might get a few tens of ohms for a 2.4m rod in many areas, so with a typical neutral current in the tens of amps range you are well over 200V. Where the rods would help is for a PME fault on a large section of the DNO network, then having 50+ rods and some balance between the 3 phases would keep the fault voltage down to safe level.
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

ppelec100

Arms
~
Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Building regulations questions.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
ppelec100,
Last reply from
pc1966,
Replies
20
Views
3,215

Advert