Hi Guys,

If i remember rightly, when doing cable calcs , first you work out the design current , say it was 47a, then you take it upto the nearest fuse size 50a, then look in tables to find correct cable csa.
Going on the above scenario ,say it was ref method c , page 131 O.S.G gives you a csa 0f 10mm square, if im reading correct .

At 46a it is 6mm square just outside .

Regards

Locket
 
Cheers Malcolmsandford,

Reason i asked the question is because on a part p course im on at the momment tutor asked us to work that scenario out above for 47amp, when i gave the answer as 10mm cable with a 50 amp breaker he said i was incorrect, he said it wouold be a 45a breaker with a 6mm cable. I was shown at college to go upoto the nearest breaker size ,then choose the corraect cable size as i did above. i thought In is equal to or greater then Ib as i was shown .


Regards

Locket
 
on site guide is good for learning, even section that you follow and gives a distance to stay within and vd and efli all buit in think around pg 58-9
 
Cheers I=P\U

Thanks for clarification, ijust wondered why the tutor who seems very experieced would have dropped it down to 45a breaker and used 6mm cable it dosent measure upto what ive been taught , am i missing something


Regards

Locket
 
6mm will carry 47 if clipped direct, not buried under insulation. a 45A MCB will be happy at 47A, but thats pushing it a bit. suppose the cable were running a shower and a few meters were in the attic, then a mountain of itchy-poo was laid over it. i would be inclined to use 10mm to be on the safe side.
 
Cheers Telextrix,

That may be the case through experience as nodoubtyou have but for anovice like me sticking to what ive been taught and using the tables it gives me a 50a breaker with a 10mm cable, what is the point of using the tables if it can be minipulated.


Regards

Locket
 
i always say, if in doubt, go bigger option. better to under run cables and MCBs than over run. it's like your car. if you thrash it at 5-6000 revs all the time , it won't last as long as if you treat it sensibly.
 

Reply to Cable calcs in the Australia area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
915
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
515
Hello, hopefully ive got this right but if someone can check over my maths for me, id appreciate it. Im needing to install a new supply cable...
Replies
3
Views
897
I'm reading a thread at the moment about a 9.8kW shower that has been installed on a 6mm cable. My natural instinct was to think that's wrong, it...
Replies
22
Views
6K
I don't think I've ever come across a cooker that needs 10mm but I may err on the side of caution with this one. Rangemaster Leckford deluxe 110cm...
Replies
40
Views
29K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock