Search the forum,

Discuss Campsite Electric Hook-up connection in the Australia area at ElectriciansForums.net

D

dunny1234

Looking at a job on a farm campsite. They require hookup's for 18 touring caravans in a field thats 85m long (9 caravans up one side, and then 9 caravans down the other) . An approx. calculation is that i need 250m of 16mm swa cable. I'm looking at using 16a 2way hookup unit/rcbo's for every 2 caravans. Not done anything like this before, any advice would be great. Do you think 16mm swa is enough. Thanks
 
assuming a 10A supply for each caravan that's 90A without diversity. 10mm XLPE SWA is rated at 81A ( AEI Cable Finder Wizard ) so should be sufficient ( and a hell of a lot easier to install). volt drop could be an issue here though.
 
Last edited:
Thanks teletrix. I suppose 10mm swa would be cheaper too, the farmer would like that. But, volt drop over 250 metres is a concern. I told the farmer roughly what 16mm swa would cost and he seemed okay. Might as well be safe. What do you reckon? Thanks again
 
are you doing it in 1 run or 2? i would either run 2 radials, 9 vans each, or make a ring.
 
I reckon you should do the calc's required for this installation, especially those regarding ''volt drop''

The farmers incoming supply is almost certainly going to be PME/TNC-S, so it's gong to have to be TT systems. Maybe linking them all up on each line of caravan pitches will give you decent Ra values that you can work with....
 
I reckon you should do the calc's required for this installation, especially those regarding ''volt drop''

The farmers incoming supply is almost certainly going to be PME/TNC-S, so it's gong to have to be TT systems. Maybe linking them all up on each line of caravan pitches will give you decent Ra values that you can work with....
i,m just wondering how to calc. volt drop on an install like this. assuming 1 or 2 radial circuits, the load is taken at varying points, i.e. the load at the end of a run is not the total load. (only 10A if each van has a 10A supply) so would you use 10A for the full cable length, and calculate say at 50% of the length at say 30A ( allowing na bit of diversity)
 
I recently did a similar job although in a boating marina, its amazing the distance and volt drop. We allowed about 8 -10 amps per boat over 230 mtrs and ended up putting 25mm in. Our incomer was a TN-S system but due to the distances and the fact the hook up posts each had RCD built in we TT'd every post and also we protected the SWA with a 300ma time delay RCD
 
Remember, if direct burial the correct trench depths, and correct materials are used for back filling. DON'T let the farmer back-fill with just the excavated earth from the trenches!!! Better to duct the cables, but then costs go up!!
 
I'm struggling with how much diversity / calcs on this cable design. Taking full whack (which isn't going to happen) 18 x 16A = 288A and cable size for that is 95mm2 plus! The farmers going to have a heart attack when i tell him how much thats going to cost. surely thats not right
 
i,m just wondering how to calc. volt drop on an install like this. assuming 1 or 2 radial circuits, the load is taken at varying points, i.e. the load at the end of a run is not the total load. (only 10A if each van has a 10A supply) so would you use 10A for the full cable length, and calculate say at 50% of the length at say 30A ( allowing na bit of diversity)


On a radial circuit, your biggest loading is at the first point, 9 x caravans at 10a =90A. Second Point 8 x 10A =80A , and so on. To conduct a diversity exercise you will need some experience of such caravan installations, which i'm sorry to say i don't have. Maybe someone here on the forum, will be able to help on that score for you....

The volt drop calculation is similar to those or a row of lights so distance x load at each point along the circuit then combine the totals
 
Last edited by a moderator:
as a rule of thumb, i would apply 50% diversity, as i can't imagine average load for 9 caravans > 5A average at any one time. that's mt guesstimate. someone might prove me wrong. it's something i've not come across before, except one site where 4 caravan pitches were taken from the car park lighting which was on a 10A MCB. he wanted me to sort out the"nuisance tripping" of the MCB. FFS.
 
The farmer will have loads of rolls of the ducting needed to bury the cable in, so wont need to buy more, its something pretty much all farmers keep a large stock of, and he will probably have his own digger as well, so he will be able to sort out any trenches that need digging....
 
Just wondering doesn't each socket outlet at the caravan pitch need individual overcurrent protection? so would not be able to do it in a ring or radial?
 
Just wondering doesn't each socket outlet at the caravan pitch need individual overcurrent protection? so would not be able to do it in a ring or radial?

Correct me if ime wrong but I thought the discussion was ring or radials feeding a rcd,mcb connection points to each pitch with maybe metering included? That's what I thought would be required? Although as you say hasn't been mentioned.
 
Just wondering doesn't each socket outlet at the caravan pitch need individual overcurrent protection? so would not be able to do it in a ring or radial?

How do you know if these Caravan supply units don't incorporate an MCB, as well as the RCD?? Personally i don't know, but i would assume that they will!!! Maybe a DP RCBO even....lol!!!
 
Last edited by a moderator:
Just checked over the regs i think i read it wrong i thought it meant each socket had to be on a seperate circuit/cable. my bad lol.
 
I would like some bright spark to explain the volt drop equation for me in this circumstance, basicly if each point is rcd,mcb etc protected then isn't it just a bunch of sub mains connected together?
 
Thanks for all the comments. I think this job is a bit beyond me, but i'm going to give it a go. Great learning curve as i've never done a job like this. I'll be using 16a electric hookup units (rcbo) Caravan Park Electrical Services - Touring Sites on a ring around the field to connect all 9 units (each suppying 2 caravans, 18 total).

Total length of cable needed will be 250m for the ring and looping in/out of hookup units. The farmer is telling me he has had a design in for the finished park from a caravan site type installation company last year and they proposed to link between caravans with 16mm two core SWA. I reckon 25mm 2core swa would be more adequate allowing for volt drop over that distance. Obviously, I'm worried now because quoting using 25mm swa is going to be a lot more than his previous quote.

Would 16mm be adequate? Help, it's giving me a headache
 
Go for 25mm mate. Then explain to the farmer he can add extra caravans at a later point, If he uses 16mm this wont be a option. I sure he ll make the choice for you then :)
 
you need to arrive at a sensible max. current, allowing for diversity. i can't see a total load of more than 40% of total i.e. 72A. in which case 16mm XLPE on a ring is more than adequate. someone with better design technical knowledge than myself may disagree. as i said earlier, volt drop may be the deciding factor.
 
We've worked on a few sites, where calcs have been carried out by companies that specialise in Caravan sites. That kind of run is usually quoted as 25mm minimum, usually they like to see 32mm but that can be a little overkill! Also is it a single phase supply or 3 phase? if it is a 3 phase supply, would it be better to spread the load over all three?

It is amazing how much power people use in these caravans! I've seen 80amp fuses blow which cover 10 or so pitches. people leaving 2kw blow heaters on all day to keep their awning warm while they're out!

What we did to combat this stiruation was to install prepayment meters at each pitch, the campsite owner could not believe how much money he saved on electricity! and his gas sales went up too.
 
When I did my install, the cable run was protected by a 40 amp circut breaker, it was a 25 mm SWA, then whenever I got to a post I split the armoured cable open, without cutting the cores and attached a 6mm cable to feed each post. So that gives all the cables protection for the size and also you have covered yourself on the volt drop. Much better than cutting the cable and making off into boxes etc. Its really a bit like the supplier would do in the road.
 
hi

i was wondering what sort of ball-park figure it would cost to install 40 hookups in a field? starting from scratch. I'm considering getting hookups installed to start a site...

thanks
 
After some thought, I've decided to go with 2 radials. There's a 3 phase, 1 for the toilet/shower block, and i'm going the use the other 2 phases of each radial (1 phase for 9 caravans)

The caravan site require hookup's for 18 touring caravans in a field thats 85m long (9 caravans up one side, and then 9 caravans down the other) . An approx. calculation is that i need 200m of 16mm swa cable. I'm looking at using 16a 2way hookup unit/rcbo's for every 2 caravans. I think 16mm swa is enough, very slim chance that all 9 caravans will be using 16a all at once, and 16mm over 85m should cover volt drop issues Any thoughts? Thanks in advance
 
Last edited by a moderator:

Reply to Campsite Electric Hook-up connection in the Australia area at ElectriciansForums.net

Similar Threads

I have a small caravan park with 8 pitches. Each have a Rolec Electrical Hook-Up unit fitted with a Rolec 16A Single Pole and Neutral 2 Module C...
Replies
14
Views
2K
I'm sure this will have been covered before but please bear with me. Have been asked to replace a main Distribution board for a fairly small...
Replies
23
Views
5K
Bought a house a few months ago and would like to have access to electrical outlets in the garage. There is already an electric cable running to...
Replies
21
Views
2K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
576
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views