Today i was asked to have a look at an isolator that has been vandalised.The job was at a motorway service station. It has a walkway linking one station from one side of the motorway to the other which contains 12 lights along the walk way/bridge. The fused isolated is half way up one side of the ramp and has had the fuse and fuse gaurd removed ,I think it is a wilex model. We later found another isolater in a column that feeds the walkway isolater.I have switched this off hence making the walkway isolater safe.
I am assuming that the walkway isolater was put there as a type off local isolation, but I don't think it is suitable for the chosen location.
The client wants me to get these lights working ASAP. But I feel I should test the circuit before doing so which would mean opening all the lights and disconnecting what ever may be before the isotaters,and firstly finding the supply.
my question , on the walk way, remove the wilex isolater, fit a junction box housing an rcbo. Test Zs on armoured supplying walk way. Do r1 r2 test on out going lighting cable and limited insulation resistance test .
The whole things looks a mess and would prefer to stay away from it would be grateful for your help
 
i would assume that RCd protection is not reqiuerd in this situation. if you don't feel confident, then either get someone in to help you or walk away.
 
  • Like
Reactions: 1 person
Is it only the isolator thats broken and Is it vandalised or has someone isolated it
it away for maintenance. Check that first!
What type of fittings are they?
 
is that a spark from bristol, or a spark with bristols? the difference could amount to a couple of points.
 
  • Like
Reactions: 3 people
I could let that handsome chap have a look at it alright but tomorrow is macydies day so I don't think he'll be up much the fat *******!
 
  • Like
Reactions: 1 person
To answer you scottysparks they are fluorescent fittings and I have asked the question wether or not it has deffinetly been vandalised or not but am waiting for an answer.
 
scottysparky???????? I am a Scotsman and alays will be and will be belting out Flower of Scotland on Sat when you go running in your "sweet Charriots":fuk2:

regards

SCOTsparky up near Glasgow:joker:
 
Before you do anything check if this so-called vandalised switch fuse has been taken out of service for maintenance purposes. Though i can't think why anyone would take the fuse carrier away, as well as the fuse!!!! lol!!

If the isolator in the post feeding the walkway is also a switch fuse, just replace the damaged switch fuse with a lockable rotary isolator!!
 
As Mike says above.

Have walked away before ( not often) . But trust yerz gut.

especially if yours is expanding into a panis like mine, more to trust. Alot more.
 
Last edited by a moderator:
  • Like
Reactions: 1 person
scottysparky???????? I am a Scotsman and alays will be and will be belting out Flower of Scotland on Sat when you go running in your "sweet Charriots":fuk2:

regards

SCOTsparky up near Glasgow:joker:

how many international rugby tournaments have scotland won again ?

go choke on yer haggis while Manu Tuilagi stomps on your back line.

;-D
 
  • Like
Reactions: 2 people
how many international rugby tournaments have scotland won again ?

go choke on yer haggis while Manu Tuilagi stomps on your back line.

;-D

Well,they didn't win the last six nations
Oh and the English and Irish couldn't cope with it either,that leaves just one team,now I wonder who :clap:
 
  • Like
Reactions: 1 person
Well,they didn't win the last six nations
Oh and the English and Irish couldn't cope with it either,that leaves just one team,now I wonder who :clap:

you would like to step into my dedicated rugby thread in chit chat to discuss this further ?




*polishes knuckle-duster while humming swing low.
;-)
 
  • Like
Reactions: 1 person
Valid point about the isolater but I am dubious if I do that and energies the circuit how do I know that what ever is protecting that circuit will trip out in the correct time.ie meet the required Zs times. If i took a Zs reading from the isolater to be replaced and found a high reading would it not be best to put an rcbo in a jb to ensure it meets the Zs times and provides further safety.
or is this over kill.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Can I use an rcbo
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
18

Thread Tags

Advert

Thread statistics

Created
Proper Job,
Last reply from
Proper Job,
Replies
18
Views
2,883

Advert