Why would there be 2x4mm @Adam W ? I'm running dedicated radials, 16A breaker, single socket (for a single 13A appliance), 1x2.5mm.

As for the FCU question, I'd have thought it would have been obvious from the information I've posted already. This is a sports hall. Having blow heaters lying around the floor when little Johnny is playing footy isn't going to be very useful. On plugs, they can plug them in when the room is due to be used for exams, unplug them when due to be used for sports.
 
Maybe, but 3000/240 = 12.5, 240v being more like what you actually get in the UK. 2x2.5mm are easier to terminate than 2x4mm. If the ring only consisted of FCUs supplying heaters then that would make it a "dedicated circuit" would it not?

Hmmm good point, thanks. Remind me, what reg is it that says we're allowed to design by 240v again? I forget.
 
Think of the amount of callouts if you fitted these heaters on a 13 A fcu
3000W /230 =13.04A mps wouldn't take long to blow those would it, an why Ring Final, what's the point? plus the BS 7671 RECOMENDS that a fixed load of plus 2KW would be better on a dedicated circuit.
They would take a bit of 'blowing' but, from what I've seen, the plug/sockets would be giving a fair bit of heat off.
One place has one on a 4mm radial (a couple of other sockets involved) no fuse problems but a lot of heat at the plug....it worries them a bit.
What surprises me about these 3kw heaters is that some do come with a 13amp plug top fitted.
If you're looking to future additions, maybe 4mm2, DP switches.
 
They would take a bit of 'blowing' but, from what I've seen, the plug/sockets would be giving a fair bit of heat off.
One place has one on a 4mm radial (a couple of other sockets involved) no fuse problems but a lot of heat at the plug....it worries them a bit.
What surprises me about these 3kw heaters is that some do come with a 13amp plug top fitted.
If you're looking to future additions, maybe 4mm2, 20amp DP switches.
 
As others have said i would go for 16 amp sockets id go for the gwis switched interlock ones as they can take a good bashing from them pesky kids
 

Reply to Checking installation methods of RFC in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
309
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
  • Article
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
Replies
0
Views
116
Hello everyone, Back again after receiving great advice for the bathroom a few months back. This time I'm making a mess in the kitchen. We have...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock