Just checked my small portable generator (2.2kVa) and the body of the machine is not common with the Neutral terminal as mechelec suggested.

I will be maiking up a bespoke lead for this emergency duty anyway, so will connect the nuetral & earth together at the generator plug to allow the RCD protected circuits to operate as normal on the consumer unit.
 
I will be maiking up a bespoke lead for this emergency duty anyway, so will connect the nuetral & earth together at the generator plug to allow the RCD protected circuits to operate as normal on the consumer unit.


Seems your easiest option.

Just install your earth rod and away to go.:)
 
That is pretty good details about the UK useage with generators however I will give you both USA and France verison of generator useage.

USA side

There are few ways it can be done .,

Manual changeover

Automatic changeover

Localized conneciton

For manual changeover it is most common and cheaper than automatique changeover useally by few hundreds Euros even thousand Euros with larger units.

However the typical North American standby manual units typically use any generator from 7.5Kw to 15 Kw { 12.5 Kw is most common } some are cord set up and some are hardwired units but pretty good percentage of homeowner do have portable gennys they are typically from 3 to 8 Kw size { half of the time they don't work due they never exerized it at all }

For Automatique set up due the current code { regualations } they have to be sized to matched the service size in USA side typically 200 amp service will require 48 Kw generator :eek: and IMO that is plain silly and will cause serious issue espcally with diesel units and I know I did check the total load what they normally load it up and they don't go over 50~70 amp the most ditto with 100 amp service which they require 24 Kw genny that is alot more than it need to be used.

It is fine for Hosptail or large industrail useage where they can sized the unit to pick up the whole load

France verison

We do have manual or automatique changeover point switch some are before the CU and some after the CU to size it I useally sized it under the max rating of CU unit.
The reguations is almost simauir to your UK reguataions

Merci,Marc
 
Quick Update:

The Transfer switch is now ready after the addition of a multifunction meter which will display, volts, amps. kW and frequency.

I have wrote to EDF Energy seeking permission to install the switch in the external meter cupboard, if this is declined, I have a little bit more work to do, but it will fit local to the CU.

I have a picture for your entertainment :)
 

Attachments

  • P1020021.jpg
    83.6 KB · Views: 64
Nice looking unit and may i say a very tidy office/desk wish mine looked like that. How will you wire the MCB to make sure only the specified circuits get transferred? My uncle has a similar thing done I dont know how its wired it was put in as part or a rewire/upgrade he had done and he had the genny out to run some bits while the board was changed and the spark said he could aire it in for him but i dont know how it was gone and doubt he does i think there is a large SWA running from garage where genny is to the house in addition to the SWA feed to garage.

In fact I have just bee having a google on the subject quite interesting really just been looking at LGP conversions for gen sets (ideal in a fixed install and cheaper to run if its used regularly and easier to change fuel over while genny is running...

found a useful american guide here PM: INSTALLING A BACKUP GENERATOR: MARCH 98

lpg kits here Edge Technology - Benefits of LPG Gas.

Auto changer over regulator TPA - ACR6 Two Cylinder Automatic Changeover - LPG Calor Gas Propane Regulator (TPA01) - Auto Change Over Va

now just need an auto changeover for the power and apart from checking the tanks its fully automated power backup....

This looks ideal Honda EM5500s electric start generator + dual fuel LPG on eBay (end time 29-Jan-10 14:01:15 GMT)
 
Last edited by a moderator:
Quick Update:

The Transfer switch is now ready after the addition of a multifunction meter which will display, volts, amps. kW and frequency.

I have wrote to EDF Energy seeking permission to install the switch in the external meter cupboard, if this is declined, I have a little bit more work to do, but it will fit local to the CU.

I have a picture for your entertainment :)

Excellent information on your setup. I'm carrying out a similar setup but am starting from scratch on a new build. I've been researching transfer switches and best manual one seems to be the B&S one. Expensive though! Like the setup you have and wonder if you can tell us how you wired up the switch with the multi meter and what the connections look like inside?

During my research I came across this control panel which is roughly the same price as the B&S but seems to offer much more and has an auto changeover.
Automatic Generator Transfer Switch Controller with Metering

I've emailed the manufacturers to see if this would be suitable in a domestic situation. Anyone have any comments on the above system and whether it could be utilised with normal 25mm meter tails as the mains feed?
 
As the use of this project will hopefully be so infrequent that it doesn't warrant an auto starting generator, but that peice of control kit looks really good.

I have written a procedure, prior to use, and in that it lists the breakers to isolate before starting and transfering load to the generator to prevent overloading, the spliting of essencial loads can be manually managed in my case.

I have attached two pics, one showing the rear of the power meter, the other the connection arrangment.

Tip: Don't trust the meter template that comes with the instructions to be accurate grrrr, centre punched through the template, marked out, drilled, only to find the holes were out, luckily the front covers up the mistake.

Connection wise, I have used bootlace ferruls on the cables to make them tidy, neutral uses a straight through DIN rail mounted connection, the live passes through a fused DIN rail mounted connection.

I did have to extend the current transformers connections to allow the lid sufficent slack to be moved out of the way during serviceing at a later date.

The sleeving has a conductive drain wire, hence the use of a pyro copper clip to earth.

Thanks for the links and info, I found loads of stuff on youtube about the connection and use of home generators, was seriously sad, sat infront of the lappy, headphones on listening to some guy in a check shirt talking about his setup :)
 

Attachments

  • P1020018.jpg
    85.9 KB · Views: 38
  • P1020019.jpg
    91.7 KB · Views: 38
Thanks for the links and info, I found loads of stuff on youtube about the connection and use of home generators, was seriously sad, sat infront of the lappy, headphones on listening to some guy in a check shirt talking about his setup :)

Thats me most of the time....Oh to have the money to buy a shell and do it properly... :eek:

http://www.smartpowershop.co.uk/UserFiles/File/pdfs/X008_00003.pdf is nice only missing (although easily doable) is the GSM modem to send SMS or call to alertl you gen set is active and running...

I have a client who was thinging of UPS for his security system and has a genny on site (was being used before mains connected and i recon the Auto start unit is cheaper than a UPS) May need a small UPS for change over.

A mate who used to engineer in hotels had cathedral gensets and massive power factor correction capacitor banks they used to kick the genny in regularly to keep the load on the grid down to specified amounts but that used air breakers a bit over kill for a house?
 
Last edited by a moderator:
Excellent information on your setup. I'm carrying out a similar setup but am starting from scratch on a new build. I've been researching transfer switches and best manual one seems to be the B&S one. Expensive though! Like the setup you have and wonder if you can tell us how you wired up the switch with the multi meter and what the connections look like inside?

During my research I came across this control panel which is roughly the same price as the B&S but seems to offer much more and has an auto changeover.
Automatic Generator Transfer Switch Controller with Metering

I've emailed the manufacturers to see if this would be suitable in a domestic situation. Anyone have any comments on the above system and whether it could be utilised with normal 25mm meter tails as the mains feed?


Andy,

Save your money and slot this little baby in :)

[ame=http://www.youtube.com/watch?v=1j8rQEOf6zE]YouTube - Double pull Double Throw Changeover switch.divx[/ame]
 
I have read on forums that you are not permitted to install consumers equipment on a meter cupboard board, is this a fact? or urban myth?, if fact, a point of referance would be good.

I have made numerous phone calls trying to confirm or otherwise to my electricity provider and network supplier and both are passing me back an too.

Guidance notes recommend not doing it, but that is all they are, and that is inconsistant!

My generator transfer switch will hopefully live in the meter cupboard if their are no red cards.

Any help would be good

Cheers
 
I have read on forums that you are not permitted to install consumers equipment on a meter cupboard board, is this a fact? or urban myth?, if fact, a point of referance would be good.

I have made numerous phone calls trying to confirm or otherwise to my electricity provider and network supplier and both are passing me back an too.

Guidance notes recommend not doing it, but that is all they are, and that is inconsistant!

My generator transfer switch will hopefully live in the meter cupboard if their are no red cards.

Any help would be good

Cheers

It seems to vary from one DNO to another. That's not much help I know but from my own research there isn't really a definitive answer. I've had a verbal assurance they don't mind provided you don't interfere with their equipment. In essence, for my new build, I bought the meter box which came with the back board. The DNO simply installed the meter and cutout into it. From my point of view, I own the meter box and can therefore put what I want in it provided it's safe and is not against any specific regulation. However the DNO could ask you to remove non standard equipment if they came to inspect or change the meter.

I think you'll find it hard to get a common opinion on this and, as stated, some DNOs allow it and others say no. If I was you, I'd install the switch in the meter box and take the chance. Sounds like you've done your best to confirm what they allow.

Good luck and let us know how the install goes.:)
 
I spoke to EDF (my DNO) several times and they were only interested to the service head, but they would not confirm in writing that is was acceptable (or conversley, that is was not)

Maybe I'm looking to deep into this!

Last thing I want is for the meter reader to flag up a problem, chances are I will fit it in the cupboard.
 
Update 5/2/10.

E.ON confirmed over the phone that their would be no charge to move the isolator 3" to make way for a Transfer Switch.

Seimens Meter Man turns up with 'connect & test' on his job card, not move the isolator!, he said that I can't put my equipment in the meter cupboard in case the room was needed for a check meter or economy 7.

Explained that I had made numerous phone calls to confirm or otherwise that it was OK for me to install my equipment and unless EDF have formally adopted my meter box, it belongs to me, and I can put in it what I wished, unless of course he knew differently and could point me to a regulation or supply T&C.

He rang his boss, who said do the job, result Spider 1 Seimens 0 :)


Pics will follow as the switch and ancillary equipment go in.
 
Just some more pics of the transfer switch decied after chatting on here that a method to announce that the utility power had restored when running on genny would be a good idea, hence the switch which when in the off position will mute the local 230v sounder.

The switch is a lockable one i.e you have to lift the toggle to allow it to either turn on or off, bit like selecting reverse on your car :), this is so it can't be knocked either on or off.

will show you a wiring picci when its loomed nice.
 

Attachments

  • P1020045.jpg
    169.8 KB · Views: 35
  • P1020046.jpg
    155.7 KB · Views: 34
Just some more pics of the transfer switch decied after chatting on here that a method to announce that the utility power had restored when running on genny would be a good idea, hence the switch which when in the off position will mute the local 230v sounder.

The switch is a lockable one i.e you have to lift the toggle to allow it to either turn on or off, bit like selecting reverse on your car :), this is so it can't be knocked either on or off.

will show you a wiring picci when its loomed nice.

Fantastic setup and very well put together. This is definitely the route I will take. Look forward to seeing the finished switch installed and working.

Will start working on my own now! :D
 
Fantastic setup and very well put together. This is definitely the route I will take. Look forward to seeing the finished switch installed and working.

Will start working on my own now! :D

Cheers Andy,

Some of the links for the kit used:

PRO SIGNAL|ABI-027-RC|PIEZO BUZZER, MAINS VOLTAGE | Farnell United Kingdom
TYCO ELECTRONICS|FTN59|SWITCH, DPDT, LOCKING | Farnell United Kingdom
230V Green LED for Switch Panel

Expandable sleeving from ebay

If anyone wants the lable template its created in Visio, I can PM it out
 
Cheers Andy,

Some of the links for the kit used:

PRO SIGNAL|ABI-027-RC|PIEZO BUZZER, MAINS VOLTAGE | Farnell United Kingdom
TYCO ELECTRONICS|FTN59|SWITCH, DPDT, LOCKING | Farnell United Kingdom
230V Green LED for Switch Panel

Expandable sleeving from ebay

If anyone wants the lable template its created in Visio, I can PM it out

Thanks for the links. That saves me a lot of time sourcing the components. I'd love a copy of the template. The only thing I might change on mine is putting in a three position rotary switch for Mains, Off & Generator. That means I can isolate all power if I need to work on the main CU. Obviously yours would do this as well if you switch to generator and the generator isn't running! :eek:
 
(however it is based on a floating earth)

As your system is a TN-C-S system even when the main switch is open the earth is still connected.
If you connect an additional earth to the star point of the generator (common for island mode operation) you are in danger of introducing circulating currents into the system which could overload current caryying capacity of your main cabling.
As previously postedy others the safest and best way of connecting a generator is via a change-over switch (either manual or automatic)
If your generator is not expected to pick up the full load of the property you could fit undervoltage devices to all non essential circuits, that way when the mains fails the circuits will automatically disconnect; when the generator runs up to speed and closes onto the bus bar only essential cisrcuits are still connected.
 

Reply to Connecting a generator to essencial circuits in the Australia area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock