(however it is based on a floating earth)

As your system is a TN-C-S system even when the main switch is open the earth is still connected.
If you connect an additional earth to the star point of the generator (common for island mode operation) you are in danger of introducing circulating currents into the system which could overload current caryying capacity of your main cabling.
As previously postedy others the safest and best way of connecting a generator is via a change-over switch (either manual or automatic)
If your generator is not expected to pick up the full load of the property you could fit undervoltage devices to all non essential circuits, that way when the mains fails the circuits will automatically disconnect; when the generator runs up to speed and closes onto the bus bar only essential cisrcuits are still connected.


I propose to install a seperate earth rod connected via a 16mm conductor to the consumer units earthing bar, the single phase generator will have the neutral/earth tied at the local socket inlet for it.
 
Power Transfer Switch Conclusion:

All works now completed on my little project to install a manually operted Power Transfer Swich to allow me to supply the house from a stand-by generator.

If anyone wants any info on this project, just PM me.

Pic 1 : Completed unit in garage, took the oppertunity to change my existing local isolator, MCB & contactor supplying dado sockets for a smaller unit, allowing more room to fit the PTS.

Pic 2: Copper earth rod, 16mm to C/U earth bar

Pic 3: DNO lowered isolator giving more room for me to install the 16A generator intake.
 

Attachments

  • P1020156.jpg
    157.3 KB · Views: 45
  • P1020147.jpg
    320.5 KB · Views: 42
  • P1020145.jpg
    186.5 KB · Views: 45
just looking at the 16a socket is that an inlet socket ? if not that means you will have a standard 16a plug on the cable from the gen. with bare copper pins that will be live when gen. is running ,or is it a 16a female plug on gen. cable

yours benji
 
just looking at the 16a socket is that an inlet socket ? if not that means you will have a standard 16a plug on the cable from the gen. with bare copper pins that will be live when gen. is running ,or is it a 16a female plug on gen. cable

yours benji

benji

You are correct it is an inlet socket, As I was going to be the one who sets this up, I didn't factor the senario you put forward, in light of the chance that a shock hazard will exist, I will change this to an appliance inlet socket.


Cheers
 
you might have to fit it into your sw.socket as i don,t think they do a sw.outlet socket ,but it will prob. be cheaper to fit one into existing unit

yours benji
 

Reply to Connecting a generator to essencial circuits in the Australia area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock