Ignoring the obvious safety aspects - I finally fixed a socket today in a relatives home where an earth wire had come out of the connector which made the dishwasher, kettle and toaster give them shocks if they didn't have rubber shoes on...great!

Dangerous as that was - these devices appeared to have a current running around their metal parts - which led me to wonder...were they using anything that would register on an electricity meter? Could an "earth leak" so to speak, cost money? Or were they simply conducting through the nearest earth they could find and thus dangerous but "free".
 
Last edited:
If current flows through the live cable of the supply, the meter will read it. How that current runs back to the supply is immaterial.

Any load on the circuit causes current to flow…. And that load could be a human body.
 
Leakage costs money ,so yes

An unearthed socket is less likely to leak and more likely to be dangerous

So with those metal parts being “conductive” so to speak, it’s more likely just dangerous rather than it was constantly leaking energy?

Are there any tests that can be done for leakage?
 
Sort of.

While 1mA of leakage (which you would feel as unpleasant) is going to cost around 40p per year if it were "real" power, in most cases such leakage is due to capacitance, so the current and voltage are at 90 deg to each other causing "reactive" power and a true power meter (on that is actually computing the integral of I * V) it would not register as something to pay.

Some larger industrial plants do get charged for reactive power as well as real power, as it impacts on losses in the power generation system, etc, but in those sort of cases 40p per year is not going to be noticed!
 
I don't think I'm making too many assumptions to say the following.
While reconnecting the socket's earth has provided a 'safe way back' for the current it hasn't addressed why it was there in the first place. The appliances concerned should be PAT tested as mentioned above.
I'd also be interested whether there is an RCD protecting the installation or circuit, my suspicion is that there isn't.
I'd also want to test the circuit to check that if it is designed as a ring final circuit it is still actually a ring.

One possible scenario is that there was a socket with a dislodged earth wire, and the kitchen is wired as either a radial (point to point) circuit or a ring with another break in somewhere else. Either way this leaves a section of the circuit with no path back to earth. Then if an faulty appliance is plugged in within this section, the fault will be felt at that appliance and any others in the section of the circuit that has no path to earth as the metallic outer surfaces are all effectively joined together.

By the way if your relative lives near you I may not be too far away (Oswestry). Message me if you want it looked at.
 
But just to clarify for others who read this, the lack of an earth connection definitely will not increase the electricity bill. Leakage occurs naturally, it isn't always indicative of a fault, but how it returns to the source (via the earth connection or via a person) doesn't affect whether it registers on the meter. As Mikegh points out, a disconnected earth can actually reduce the leakage if the appliance is not earthed any otther way.

Much of the 'normal' leakage, i.e. not due to a fault, doesn't register on the meter anyway as it is capacitive and has near zero power factor. For example, a suppressor capacitor in an appliancce that leaks 1mA would create quite a noticeable tingle if you touched the casing in the absence of an earth connection. But at a pf of 0.05 it would register 0.001 * 230 * 0.05 = 0.012W and cost less than 2p per year in wasted energy even if plugged in 24/7.
 
I don't think I'm making too many assumptions to say the following.
While reconnecting the socket's earth has provided a 'safe way back' for the current it hasn't addressed why it was there in the first place. The appliances concerned should be PAT tested as mentioned above.
I'd also be interested whether there is an RCD protecting the installation or circuit, my suspicion is that there isn't.
I'd also want to test the circuit to check that if it is designed as a ring final circuit it is still actually a ring.

One possible scenario is that there was a socket with a dislodged earth wire, and the kitchen is wired as either a radial (point to point) circuit or a ring with another break in somewhere else. Either way this leaves a section of the circuit with no path back to earth. Then if an faulty appliance is plugged in within this section, the fault will be felt at that appliance and any others in the section of the circuit that has no path to earth as the metallic outer surfaces are all effectively joined together.

By the way if your relative lives near you I may not be too far away (Oswestry). Message me if you want it looked at.

Hi Tim,

It was indeed a dislodged earth wire - there is a 2 socket spur coming from the plug which the dishwasher was plugged into.

One of the two earth wires had disconnected from the connector block. Not great as they'd left it that way for YEARS!

Always looking for a reliable local spark though so i'll keep you in mind, doing lots of renovation work myself!
 
But just to clarify for others who read this, the lack of an earth connection definitely will not increase the electricity bill. Leakage occurs naturally, it isn't always indicative of a fault, but how it returns to the source (via the earth connection or via a person) doesn't affect whether it registers on the meter. As Mikegh points out, a disconnected earth can actually reduce the leakage if the appliance is not earthed any otther way.

Much of the 'normal' leakage, i.e. not due to a fault, doesn't register on the meter anyway as it is capacitive and has near zero power factor. For example, a suppressor capacitor in an appliancce that leaks 1mA would create quite a noticeable tingle if you touched the casing in the absence of an earth connection. But at a pf of 0.05 it would register 0.001 * 230 * 0.05 = 0.012W and cost less than 2p per year in wasted energy even if plugged in 24/7.
Thanks - very interesting and all makes sense.
 
But just to clarify for others who read this, the lack of an earth connection definitely will not increase the electricity bill. Leakage occurs naturally, it isn't always indicative of a fault, but how it returns to the source (via the earth connection or via a person) doesn't affect whether it registers on the meter. As Mikegh points out, a disconnected earth can actually reduce the leakage if the appliance is not earthed any otther way.

Much of the 'normal' leakage, i.e. not due to a fault, doesn't register on the meter anyway as it is capacitive and has near zero power factor. For example, a suppressor capacitor in an appliancce that leaks 1mA would create quite a noticeable tingle if you touched the casing in the absence of an earth connection. But at a pf of 0.05 it would register 0.001 * 230 * 0.05 = 0.012W and cost less than 2p per year in wasted energy even if plugged in 24/7.
I find when I use my laptop off the mains (two pin flex into PSU so double insulated, no earth) I get a 'tingle' off the casing of the laptop. Nothing shocking(!) but noticeable if you look for it. I am assuming this is due to some form of capacitive coupling across the PSU leaking voltage through onto the LV side then earthing through my body. The sockets I normally plug into are all on RCDs but I expect as this coupling is not causing current loss from the primary side they would not register this as a fault.
 
I find when I use my laptop off the mains (two pin flex into PSU so double insulated, no earth) I get a 'tingle' off the casing of the laptop. Nothing shocking(!) but noticeable if you look for it. I am assuming this is due to some form of capacitive coupling across the PSU leaking voltage through onto the LV side then earthing through my body. The sockets I normally plug into are all on RCDs but I expect as this coupling is not causing current loss from the primary side they would not register this as a fault.
Yes same, with any unibody Apple laptop. You can touch it with one hand and touch someone else with the other and feel the electricity.

I've had musician friends have trouble with earth loops causing hum and buzz in sound paths because there were too many earths in the loop and often having to remove the earth from the plug itself to stop it.

It's interesting because in the US where it's designed they don't use ground pins - so whilst it's a universal charging adapter it was designed in a country that just uses a 2 pin plug!
 
Yes same, with any unibody Apple laptop. You can touch it with one hand and touch someone else with the other and feel the electricity.

I've had musician friends have trouble with earth loops causing hum and buzz in sound paths because there were too many earths in the loop and often having to remove the earth from the plug itself to stop it.

It's interesting because in the US where it's designed they don't use ground pins - so whilst it's a universal charging adapter it was designed in a country that just uses a 2 pin plug!
@ DanShepard yes we do use ground pins. What you are referring to is many many years ago they didn’t have equipment grounds and now I do a lot of work and keep running into this situation and it’s frustrating and yes it’s dangerous.
 
I did an RCA test on the socket this morning and I did trip off at the main switch on the consumer unit. Not sure why the lack of earth wasn't doing that, but it appears to be passing all tests at the moment.

Voltage between Neutral and Earth is reading 00.7v
 
The sockets I normally plug into are all on RCDs but I expect as this coupling is not causing current loss from the primary side they would not register this as a fault.

You can touch it with one hand and touch someone else with the other and feel the electricity.

This is indeed genuine leakage current coupled over from the primary side and it is sensed as leakage by the RCD, but the current is much to low to cause a trip. You can feel a fraction of a milliamp order some conditions, and many PSUs are designed leak that much. The actual leakage amount is a compromise between reducing radio interference and leaking enough to be annoying (but not in any way dangerous.) By the time you get up to 'fault' levels high enough to trip an RCD (tens of mA) that is quite a hefty jolt, not just a tingle.

I've had musician friends have trouble with earth loops causing hum and buzz in sound paths because there were too many earths

There are usually better solutions than disconnecting the safety earth. Having worked in professional audio for many years and designed and wired a lot of studio equipment, I can honestly say that I have never had to leave something floating, I have always been able to avoid the earth loop some other way. Hum problems are also often blamed on earth loops that are actually due to something else entirely,

It's interesting because in the US where it's designed they don't use ground pins -

As Megawatt says, all modern US installations have grounds everywhere and grounded outlets have been in use for 100 years. There is some important history behind the 2 / 3 pin plug adoption and it's as much a European thing as American. Basically most plug/socket systems allow for either 2- or 3-pin plugs and mains adaptors, that fit into 3-pin sockets. In the US if your device doesn't need a ground, it has a NEMA 1-15 2-prong plug that fits a 5-15 or 5-20 3-prong receptacle and simply doesn't use the ground connection. This is what you see on chargers etc. But a grounded appliance will have a 5-15 or 5-20 3-prong plug fitted as standard.

Likewise in Europe a double-insulated low-power appliance gets a 2-pin Europlug that will fit any of the European variants that have pins on 19mm centres, and just ignores the available earth contact whatever form it happens to be. But class I appliance will be fitted with the locally suitable earthed plug.

In the UK we used to have both 2- and 3-pin round-pin plugs in all three current ratings (2A, 5A and 15A) but they were not compatible. The line and neutral pins were the same size but the 2-pin version had slightly smaller spacing between them. So a 5A 2-pin plug could only be used in a 5A 2-pin socket. Then in 1947 we had a major re-design and got rid of all of those old systems, which is something very few other countries have done. At that point we introduced mandatory safety shutters that were, at first, always operated by the earth pin, so there was no possibility to include a 2-pin 13A plug variant. It's the only system where one has to use a bulky 3-pin plug even for tiny appliances with 0.1A load and no need of an earth. If you regularly use USA and EU plugs as I do, you come to see that as something of a drawback.
 
There are usually better solutions than disconnecting the safety earth. Having worked in professional audio for many years and designed and wired a lot of studio equipment, I can honestly say that I have never had to leave something floating, I have always been able to avoid the earth loop some other way. Hum problems are also often blamed on earth loops that are actually due to something else entirely,
As @Lucien Nunes says, professional audio kit is designed not to have this problem, typically using balanced signal connections (so shield/safety ground is not part of the signal path), but obviously in the digital age it is no longer an issue.

Disconnecting a safety earth is a really BAD thing to do, sometimes it can be fixed with 'consumer' grade kit (design wise, not always price-wise) by how the power cables are fed to take them to a single block.

I have to admit to once doing it to a laptop supply fed off a 12V inverter in a hired van used for trip entertainment on a mate's stag trip Dundee to Newquay (no cable removed, I leave it to your imagination how I butchered that one) but that was quite a specific case and not something I'm proud of. The choice of videos is another thing I'm not proud of, but it was a stag-do...

It's the only system where one has to use a bulky 3-pin plug even for tiny appliances with 0.1A load and no need of an earth. If you regularly use USA and EU plugs as I do, you come to see that as something of a drawback.
The Schuko plugs are not exactly compact either! Though I guess part of them is hidden when mated.

In reality no one really anticipated appliances taking only a couple of Watts or less, so the designs were never really optimised for it. Now you get 13A outlets with USB 5V power as a solution, though hardly universal and quality is "variable" shall we say.
 
But at a pf of 0.05 it would register 0.001 * 230 * 0.05 = 0.012W and cost less than 2p per year in wasted energy even if plugged in 24/7.
A good point to raise PF!

Perversely an ungrounded CPC that leaks 100-200k resistive to true Earth might actually cost more! While the current would be less, the PF might be significantly more. E.g. 0.75mA with 0.5 PF is about 0.09W so around 7 times higher.
 
Schuko plugs are not exactly compact either!

My point being, that in Schuko territories and indeed anywhere in Europe and elsewhere that uses round pins on 19mm centres, there is the option of a slimline 2-pin plug for class II appliances up to 2..5A. There is no obligation to use a full-size 3-pin plug on a class II appliance just to make the socket function, as there is in the UK.
 

Reply to Could an unearthed socket in theory cost money? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hiya, I live in a pretty old apartment in Japan. There's only one wall in the whole apartment that has a screw to allow to connect a power cable...
Replies
2
Views
2K
HI! I'm a disabled guy, Cerebral Palsy, Hydrocephalus, Dyspraxia and Asperger's, who's been put into (basically) a one-room flat, there is a...
Replies
5
Views
1K
Hi Electricans, I am a homeowner with an earth bonding question I am receiving conflicting advice upon and hoping someone can help point me in the...
Replies
29
Views
7K
This might be long so feel free to grab a brew. So, as some of you may know, i'm a 34 year old who has been dying to get into the industry. I...
Replies
66
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock