daiplayer

Just a thought, ; IR testing on house today , to find EVERY circiut around th 200 -300 Mega ohm mark.... apart from obviously a new one i put in.

Obviously the insulation has broken down over time. i was curious if the age of the installation could be estimated / calculated by this ?

Ok, i know that different levels of miosture / temperature within the house will effect insulation life. But still ,...would be curious to know.
 
200Mohms is better than most installations will achieve anyway. 2Mohms is acceptable, so what's your worry?
 
Just a thought, ; IR testing on house today , to find EVERY circiut around th 200 -300 Mega ohm mark.... apart from obviously a new one i put in.

Obviously the insulation has broken down over time. i was curious if the age of the installation could be estimated / calculated by this ?

Ok, i know that different levels of miosture / temperature within the house will effect insulation life. But still ,...would be curious to know.

Paragraph 1) 200-300M ohms is excellent for an in service final circuit.
Paragraph 2) No the age can't be estimated/calculated from the measured IR.
Paragraph 3) The issue is not so much that moisture/temperature will effect insulation life, but that it will effect the measurement of IR.
 
Last edited by a moderator:
Paragraph 1) 200-300M ohms is excellent for an in service final circuit.
Paragraph 2) No the age can't be estimated/calculated from the measured IR.
Paragraph 3) The issue is not so much that moisture/temperature will effect insulation life, but that it will effect the measurement of IR.

Agree entirely!!! Highly unlikely you would ever get identical IR readings from one day to the next. And as you say environmental influences will affect the readings, not necessarily the insulation life of the installation...

What regular PPM IR readings Can tell you, are tendencies towards IR breakdowns of a particular machine/motor or cable. ie, ...A is marked and continuing lowering of IR values. Normally these sorts of regular tests are only made on essential equipment or supplies...
 

Reply to Curiosity in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
A
Sorry to post such a long message but realise people need all the information so accurate conclusions can be reached. The domestic property has a...
Replies
12
Views
4K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
R
21st Feb 2014 Today I had one of the weirdest faults I’ve ever come across. My conclusion to some may sound bizarre but from what I can see...
Replies
0
Views
2K
Robospark
R

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock