Discuss distribution circuit at origin (meter tails) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

jase

On the EIC page 3 it says to record details of these on first line, would that just be on the circuit details side of the form? or do you have to fill in test results for tails too?
 
amberleaf
Respected Member


Join Date: Mar 2009
Posts: 1,046
Thanks: 0
Thanked 486 Times in 348 Posts
Re: Section - 301- Questions - Testing ,
Recording of Circuit details and Test Results for Distribution Circuits :

Regulation 514.9.1 and Chapter 63 ( Certification & Reporting ) call for circuit details and test results to be provided for all circuits in an Electrical Installation , However, there is sometimes a tendency to Overlook the provision of this information for Distribution Circuits ( or Sub-Mains as they are sometime called ) where such circuits form part of the installation . the requirement to provide such information applies to Distribution Circuits as it does to final circuits .

One Situation where this type of Omission of Data Occurs is where a Main Switch , located at the Origin , feeds a Single Distribution Circuit to a Remote Distribution Board or Consumer Unit . ► Without this Recorded Data the Certification for the Installation is Incomplete .
This does Not Apply to Meter Tails making the Short Connection between the Consumer Unit or Main Switch to the Electricity Meter or Distributor’s Isolator .

Example of a Distribution Circuit :-
Electricity Distributor’s Overload Protective Device ,
Meter Tails ,
~ Main / Switch – Switch / Fuse ,
SWA – cable ( Distribution Circuit ) ,
~ Remote Consumer Unit , ◄




Thanks amberleaf;)
 

Reply to distribution circuit at origin (meter tails) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
802
Where do people record the Ze & PFC of a 3 phase installation, if there is say 10m of 25mm tails between the 4 pole isolator (next to the meter)...
Replies
7
Views
1K
happysteve submitted a new resource: Circuit details + test results - extra sheets for EIC/EICR - BS7671 2018 + A2:2022 - Fillable circuit...
Replies
1
Views
1K
I would like to get some information on what protection is on a multi meter when accidentally testing a live circuit while the meter is on the...
Replies
1
Views
472
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock