Evening, all.

I've got a kitchen coming up that might lead to more work with a local joiner... first job with him and I want to appear on the ball.

Current set up is 32A MCB on RCD side of a split board, 6.0mm serving a regular cooker switch with only an electric oven coming off it. Hob is presently gas.

The kitchen plan asks for a built in eye level oven and separate microwave combi at the current switch position and an electric hob further round the worktop, so the 32A supply would have to be extended.

The ratings are:

Microwave - 1600W for grill, 900W for microwave. Don't know if these fiunctions would operate simultaneously.
Regular oven - 3650W
Hob - 7200W

Both ovens run off a standard 13A plug, but to have these on the rfc along with kettle, toaster, washing machine and whatever else may be a push.

My plan was to have one of the ovens on the rfc, the other sharing the cooker circuit with the hob. Possible uprating of the mcb to 40A
 
TL;DR
2 ovens, 1 hob on single circuit?
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Aico 3000
James

James

-
Mentor
Esteemed
Arms
Supporter
Patron
I personally hate diversity calc's on cooking appliances in the kitchen

the whole idea of diversity is that appliences will not all be on at the same time.
however I for-see a situation of a large dinner party or a Christmas day when unusually but not unforeseeable all of them are on at the same time.

it is unlikely to cause cable damage but could cause a breaker to trip.
at that point the customer thinks that the electrix are under spec and or faulty, that causes you problems.

I personally prefer to over spec rather than use the guidance in this particular circumstance.

years ago, you would get away with it because of the time taken to blow a fuse or fuse wire but now with breakers tripping faster and more uniformly it can cause more issues than you expect.
 
littlespark

littlespark

-
Esteemed
Arms
  • Thread Starter Thread Starter
  • #3
Ideally, I would give them all a dedicated supply from the board, but wrong end of the house. At least the kitchen rfc only serves the kitchen and not the rest of the downstairs.

Both ovens are designed to be plugged in, so i might just give them a single socket each, on the ring... (not a double to serve both) and see what happens. Leaving the hob with 32A all for itself. (31.5A for a 7.2kW appliance. That's pushing it already!)
 
James

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Ideally, I would give them all a dedicated supply from the board, but wrong end of the house. At least the kitchen rfc only serves the kitchen and not the rest of the downstairs.

Both ovens are designed to be plugged in, so i might just give them a single socket each, on the ring... (not a double to serve both) and see what happens. Leaving the hob with 32A all for itself. (31.5A for a 7.2kW appliance. That's pushing it already!)
lets face it, at least when you are in the middle of cooking a big dinner using both ovens, you are probably not doing the laundry and running the dishwasher, toaster and kettle at the same time.
but you can see why i dont like diversity in the kitchen?
 
littlespark

littlespark

-
Esteemed
Arms
  • Thread Starter Thread Starter
  • #5
but you can see why i dont like diversity in the kitchen?
Too many of them, and Ashley Banjo throwing the little one over the kitchen table? Just a nuisance!
 
Pretty Mouth

Pretty Mouth

-
Esteemed
Arms
Applying diversity you're getting a design current of 24.4A, well within your 32A. The diversity allowance for cookers has been around for a long time, you would expect it to have been thoroughly tried and tested by now wouldn't you?

Are any forum members finding they are getting nuisance tripping as a result of overload on cooker circuits where diversity has been correctly applied?
 
davesparks

davesparks

-
Mentor
Esteemed
Arms
the whole idea of diversity is that appliences will not all be on at the same time.
however I for-see a situation of a large dinner party or a Christmas day when unusually but not unforeseeable all of them are on at the same time.
That is just part of how diversity works, it is not just the fact that not all appliances are on at the same time. Especially with cooking appliances.
It is the cycling of the thermostats which plays the biggest role in diversity for cooking appliances.

Plus if you've ever cooked a meal such as Christmas Dinner you'll know that you don't cook everything at the same time, for the same length of time.
 
Ian1981

Ian1981

-
Mentor
Esteemed
Arms
The whole Christmas Day cooking dinner and every thermostat is on scenario just doesn’t exist, the whole diversity application is a time proven method applied to cooking appliances for as long as I can remember.
 
Midwest

Midwest

-
Esteemed
Arms
We had an 8kW range cooker, where the three ovens cooked all run simultaneously. Clamped it once going full pelt, never got more than 14A.

If it were me, I’d be thinking of separate radials, but I can only see you showing full load of one oven? The combi microwave, as far as I’m aware, can run the grill and microwave at the same time, which comes in around 11A, that’s why I would be thinking of it’s own supply.

Doesn’t the guidance in app 15 recommend separate supplies for cooking loads over 2kw? What’s the rating for the other oven? Could they use the existing 32A supply?
 
Marvo

Marvo

-
Mentor
Esteemed
Arms
That is just part of how diversity works, it is not just the fact that not all appliances are on at the same time. Especially with cooking appliances.
It is the cycling of the thermostats which plays the biggest role in diversity for cooking appliances.

Plus if you've ever cooked a meal such as Christmas Dinner you'll know that you don't cook everything at the same time, for the same length of time.
Also the fact that there's a substantial time delay before an MCB trips if there's a marginal overload....and even longer if the OCPD's are fuses
 
Lucien Nunes

Lucien Nunes

-
Mentor
Esteemed
Arms
Under normal conditions a B32 won't trip at 40A and will take 20 mins at 50A. During that time Ib>In so it's incorrect to rely on that buffer zone at the design stage. But if you follow the normal diversity procedures and make In>Ib based on the load with diversity applied, you've complied with the regs, for practical purposes the circuit will never be overloaded, and you've still got the buffer zone of the OCPD fusing factor to render a nuisance trip exceedingly unlikely. Even if everything is turned on at the same time, the Simmerstats and thermostats will be cycling happily before the 20 mins is up.
 
Pretty Mouth

Pretty Mouth

-
Esteemed
Arms
Doesn’t the guidance in app 15 recommend separate supplies for cooking loads over 2kw?
I read that guidance as 'don't put cooking loads over 2kw on general purpose socket circuits' (or is that what you meant?)
Post automatically merged:

Personally I'd put everything on the 6mm 32A circuit, and follow the guidance on p190 OSG.
 