The complete load is only 2.17 A assuming 100W max for each fitting though with 150W lamps you could get up to 3.26A.
 
Various points to look at here....

Mr Burns saw the fact that id specified incandescent lamps and your typical lamp in domestic of this nature will be subject to regulation 559.6.1.6 so a 30amp wire is out of the window and won't comply.

Thus we drop down to 15amp with the same question ...

Note rating of switches etc are only subject to the load they are switching and not the fuse that covers them or we would have a lot of non compliant installs out there.

Install is your basic drilled through joists buried in plaster and insulation in loft - just to clarify although it changes little.

Nick your last sentence is key to part of it...

and there is nothing to stop someone adding a ton more light fittings, so it doesn't comply....?

I thought you said we are not changing the type or number of luminaires ?
 
Apologise posts coming quicker than i can respond .... yes your PFC is a factor that could affect the answer and another point awarded for bring it up as a query but as you'll find I've carefully chosen

Small house
5 lamps
1mm cable installed in standard methods

So PFC affecting this scenario is a very unlikely situe even with a very poor PFC but good thinking!
 
I thought you said we are not changing the type or number of luminaires ?

I didn't say he was right he just that its a key point now we are not adding to the circuit or changing lamps do we have to account for other peoples future work if we changed this wire to 15amp?
 
if you are considering th ecircuit as a fixed load, then the OCPD may need to provide short circuit protection only.
 
  • Like
Reactions: 1 person
I didn't say he was right he just that its a key point now we are not adding to the circuit or changing lamps do we have to account for other peoples future work if we changed this wire to 15amp?

The simple answer to that is no, if someone wanted to add to/alter that circuit at a future date then they should be assessing that it is suitable for the intended modification.
 
  • Like
Reactions: 1 person
1mm its almost the same size as the fuse wire ,oh how often has that been used instead
 
You now have the consideration that one of the lights is in a bathroom and there has been no mention of 30mA RCD protection (701.411.3.3).
 
Yes, I would say that it would comply, so long as certain conditions are met. I ain't gonna beat around the bush.

If this work was not carried out in an installation with significant fire risks present, the circuit's Zs falls below the maximum corrected value for the new fuse, the circuit cannot be overloaded by nature of the very load itself, the cpc sizes have been calculated as adequate and the requirements for thermal constraints under fault conditions have been met, then you have confirmed that the circuit cannot be overloaded, the conductors cannot damaged under fault conditions and that disconnection times can still be met.

Would I do it??? NO! :)

Anyone answering no I would be pointing them in the direction of regulations 433.3.1.ii and 434.5.2
 
  • Like
Reactions: 1 person
You now have the consideration that one of the lights is in a bathroom and there has been no mention of 30mA RCD protection (701.411.3.3).

Aye stop that .. its an old install we are not trying to make it comply to the 17th merely answer a theoretical query that in the real world you wouldn't do for various reasons but not necessary due to regulation.
 
We have that we cannot use 30A fuse wire from 559.6.1.6
We have
433.3.1.ii that says that because five lights is a fixed load and unable to overload that the circuit only need to be protected against fault current.
The PFC is assumed to be low enough that the 15A fuse is not unable to cope (since the 5A would have been compliant). Though calculation could be done for 534.5.2.
We do not want it to comply to 17th edition, just be safe for continued use so RCD protection is not installed.

Fit and forget!
Oh yes but as DS says I would not do this in a domestic property unless they were desperate.
I have now got another desperation to go to, so signing off.
 
  • Like
Reactions: 3 people
Aye stop that .. its an old install we are not trying to make it comply to the 17th merely answer a theoretical query that in the real world you wouldn't do for various reasons but not necessary due to regulation.

But if we're talking strict compliance to the regs here for theoretical purposes, you are proposing changing the OCPD for the circuit, which means you're 'taking responsibility' for the whole circuit, hence, RCD.
 
RB pretty much wraps it up here ... totally compliant but not a practice to condone as the domestic realm is often subject to abuse and although future changes has no implication of what you did and would be down to their own responsibility it is often practiced in domestic for these reasons to provide O/L protects beyond requirements.... only a few circuits do require OL protection namely with socket outlets on them but the rest can fall under the same omit that my example uses.

I often use this OL regulation when wiring large machines to keep cable cost down but still be within regulation ... domestic it is often unrecognised that it is an option and yes i have used it to upgrade a shower without ripping out all the existing wire for no reason.
 
this all depends on a few factors cable size factors installation methods etc now if its a 1.5mm cable clipped direct maximum cable rating is 20 amps so 15amps mmm looks ok but there is the correction factor for bs3036 fuse of 0.725 so if you take it with out any other factors it would be 15 / .725 = 20.69 so over the maximum rated now if you add say 3 cables you have a grouping factor of 0.70 that would then become 15/.70 x .725 = 29.42 so my answer would be no
wrong.

1.5/1.0 flat twin method C is good for 19A....so a 15A BS3036 wouldn`t comply....would it.

OK correction:

20A

still doesn`t comply...
 
But if we're talking strict compliance to the regs here for theoretical purposes, you are proposing changing the OCPD for the circuit, which means you're 'taking responsibility' for the whole circuit, hence, RCD.

Valid point hence I tried to express it as just theoretical without stepping into other separate issues ... ok then rephrase the question that you came across a lighting circuit existing with a 15 fuse wire - can you change it for another 15amp wire leave it and comply with regs ... no alteration or upgrade has been made.
 
Ive come in at the tail end after all the juicy bits have been aired ....... is the voltage drop compliant :)

Was just bored badge and passing time ...its a small house with 5 lights ..ill let you work out if VD is a worry or not without further info' :)
 
Valid point hence I tried to express it as just theoretical without stepping into other separate issues ... ok then rephrase the question that you came across a lighting circuit existing with a 15 fuse wire - can you change it for another 15amp wire leave it and comply with regs ... no alteration or upgrade has been made.
its the corredtion factor to be applied for BS3036s

.725

so 1.5/1.0 good for 20A

20 X .725 = 14.5A

so its a non-conformance....simple as...
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Does this comply.... thinker of the day!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
51

Advert

Thread statistics

Created
Darkwood,
Last reply from
Richard Burns,
Replies
51
Views
4,306

Advert