Having a hard time figuring this one out, think I've got it but I figure best check with you guys!
On a TT system, metal CU so needs to be protected by a time-delayed RCD in the tails (to allow smaller Amp RCDs on sections of the board to trip first), and this time-delayed RCD should be in it's own enclosure. So far so good.
Now here's the catch... P.S. I bet you all just said "ahhh yes, I know what he's about to say" to yourselves and you're probably right:
If it's in a metal enclosure then if the incoming line tail faults to the enclosure then that's unprotected and the enclosure becomes live without protection, so obviously I can't do that no matter what. So it needs to be an electrically insulated enclosure, but do the 17th edition requirements for consumer units apply to this enclosure, being fire rated in particular? If so what do you recommend I use?
On a TT system, metal CU so needs to be protected by a time-delayed RCD in the tails (to allow smaller Amp RCDs on sections of the board to trip first), and this time-delayed RCD should be in it's own enclosure. So far so good.
Now here's the catch... P.S. I bet you all just said "ahhh yes, I know what he's about to say" to yourselves and you're probably right:
If it's in a metal enclosure then if the incoming line tail faults to the enclosure then that's unprotected and the enclosure becomes live without protection, so obviously I can't do that no matter what. So it needs to be an electrically insulated enclosure, but do the 17th edition requirements for consumer units apply to this enclosure, being fire rated in particular? If so what do you recommend I use?