As others have said, you should get an electrician in . In the meantime, if you know the layout of your old kitchen and where the old cooker location was, you could start looking in that area for your suspect joint (keep ringing matey boy up, 'cos they'll know). Kitchen fitter 'electricians' tend to burry their joint boxes in walls under tiles! Or you might be lucky, and it's in the ceiling void.
 
Last edited:
Not sure of Scottish requirements. Try the live to earth voltage test etc I mentioned, at all points including the incoming and outgoing sides of the switch. As Mid says, keep ringing because they may be the only person who knows if there is some hidden joint buried somewhere.
 
Just came across this thread. Requirements re certification - there's no equivalent to Part P, but the Scottish Building Regs do set out some requirements. Scheme member or not, every electrician worth his/her salt should certify the work they do.
If the o/p is still having problems, PM me and I'll have a look.
 
Just came across this thread. Requirements re certification - there's no equivalent to Part P, but the Scottish Building Regs do set out some requirements. Scheme member or not, every electrician worth his/her salt should certify the work they do.
If the o/p is still having problems, PM me and I'll have a look.

Finally got a hold of the electrician that did the initial works, the fault was a "damaged cable" apparently caused by the joiner 8 months ago, although I remain a little skeptical about this! However that said luckily the damaged cable was hidden behind the plasterboard within close proximity of the oven isolator and the cable was re-jointed and the oven is now working again. Although I am curious to why the RCB or MCB did not trip.

I was working when the electricians did the works but did instruct the wife to query with them about the certificates, they did a Billy Whizz (from the Beano) in and out before questions were asked and said to the wife "aye I will be having words with the joiner" then left.




At least we got to know the outcome of this one........ Oh yeah, we didn't lol

Well, continuous sunshine in Scotland is rare, took the advantage while I could before the Scottish winter settles back in (in about 10minutes from now!) :p
 
Finally got a hold of the electrician that did the initial works, the fault was a "damaged cable" apparently caused by the joiner 8 months ago, although I remain a little skeptical about this! However that said luckily the damaged cable was hidden behind the plasterboard within close proximity of the oven isolator and the cable was re-jointed and the oven is now working again. Although I am curious to why the RCB or MCB did not trip.

I was working when the electricians did the works but did instruct the wife to query with them about the certificates, they did a Billy Whizz (from the Beano) in and out before questions were asked and said to the wife "aye I will be having words with the joiner" then left.






Well, continuous sunshine in Scotland is rare, took the advantage while I could before the Scottish winter settles back in (in about 10minutes from now!) :p

So were you given a MWC to confirm the cable repair and the tests conducted?
 
No, just a brief explanation to the wife that the cable was damaged, now fixed thanks again cheerio.
 
Last edited by a moderator:
I thought I may either have: ...4. may be an earth leak
Although I am curious to why the RCB or MCB did not trip.

Why would you expect a high resistance connection or severed conductor do that? Unless the result was a general meltdown that destroyed the insulation and caused a short, probably revealing itself in the process with escaping smoke?

As an instrumentation engineer - you'll be aware of the input resistance of your DMM, in which case you can calculate the resistance of, and power dissipation in, the point of high resistance. Most likely, it did get hot at one stage, but soon burnt itself O/C. I am skeptical of the explanation given though!

I recall an electrical engineer telling me .... that you could potentially receive a bigger belt from the neutral than the live!

Go on, explain!
 
Although I am curious to why the RCB or MCB did not trip.
If the dodgy joint was simply providing a high resistance, which would explain the drop in measured voltage under load then (a) the MCB would not trip because the current being drawn would be well within the rated current of the device and (b) the RCD would not trip because its not a fault current to earth.

BS7671 says all work must be documented and there are model forms therin for various types of work. You should have received a certificate when the work was done originally and also when the corrective work was undertaken.

If the repair to the cable is "not accessible for inspection" (i.e buried in the wall) then the method of jointing cannot have screw terminals which can work loose. The most common forms of maintenance free joints are crimps or suitably rated push-fit connectors with sprung-loaded terminals. The joint must be contained in a box providing mechanical protection and it should have strain relief clips on the incoming and outgoing cables.
 
I would say that it is obviously a loose connection as it would be an achievement to undersize cables enough at a great enough distance to lose 90V in a house!

You need to get an Electrician to sort this out urgently as it is a fire hazard.
 