Finally got a hold of the electrician that did the initial works, the fault was a "damaged cable" apparently caused by the joiner 8 months ago, although I remain a little skeptical about this! However that said luckily the damaged cable was hidden behind the plasterboard within close proximity of the oven isolator and the cable was re-jointed and the oven is now working again. Although I am curious to why the RCB or MCB did not trip.

I was working when the electricians did the works but did instruct the wife to query with them about the certificates, they did a Billy Whizz (from the Beano) in and out before questions were asked and said to the wife "aye I will be having words with the joiner" then left.






Well, continuous sunshine in Scotland is rare, took the advantage while I could before the Scottish winter settles back in (in about 10minutes from now!) :p

So were you given a MWC to confirm the cable repair and the tests conducted?
 
No, just a brief explanation to the wife that the cable was damaged, now fixed thanks again cheerio.
 
Last edited by a moderator:
I thought I may either have: ...4. may be an earth leak
Although I am curious to why the RCB or MCB did not trip.

Why would you expect a high resistance connection or severed conductor do that? Unless the result was a general meltdown that destroyed the insulation and caused a short, probably revealing itself in the process with escaping smoke?

As an instrumentation engineer - you'll be aware of the input resistance of your DMM, in which case you can calculate the resistance of, and power dissipation in, the point of high resistance. Most likely, it did get hot at one stage, but soon burnt itself O/C. I am skeptical of the explanation given though!

I recall an electrical engineer telling me .... that you could potentially receive a bigger belt from the neutral than the live!

Go on, explain!
 
Not sure of Scottish requirements.
Certification as per BS7671 and in certain circumstances a Building Warrant could be required.

no certificate for work done and a balder-dash explanation makes you wonder if they were sparks?
 
  • Like
Reactions: 1 person
Although I am curious to why the RCB or MCB did not trip.
If the dodgy joint was simply providing a high resistance, which would explain the drop in measured voltage under load then (a) the MCB would not trip because the current being drawn would be well within the rated current of the device and (b) the RCD would not trip because its not a fault current to earth.

BS7671 says all work must be documented and there are model forms therin for various types of work. You should have received a certificate when the work was done originally and also when the corrective work was undertaken.

If the repair to the cable is "not accessible for inspection" (i.e buried in the wall) then the method of jointing cannot have screw terminals which can work loose. The most common forms of maintenance free joints are crimps or suitably rated push-fit connectors with sprung-loaded terminals. The joint must be contained in a box providing mechanical protection and it should have strain relief clips on the incoming and outgoing cables.
 
I would say that it is obviously a loose connection as it would be an achievement to undersize cables enough at a great enough distance to lose 90V in a house!

You need to get an Electrician to sort this out urgently as it is a fire hazard.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Experiencing volt-drop within household
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
bridav,
Last reply from
Risteard,
Replies
27
Views
4,259

Advert